Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm. Does the cable have to be the same throughout? If so what is the reg for this please. 🤔
 
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm. Does the cable have to be the same throughout? If so what is the reg for this please. 🤔
No there isn't a reg requiring consistent cable throughout a circuit. (In fact 433.3 mentions the scenario of a reduction in CCC.)
If the 6 sq mm leg was clipped direct (when it can carry 47 amps before any further de-rating) it might have complied.

Basically 433.1.1 needs to be met for the whole circuit unless over-current protection can be legitimately omitted (see sections 433.2, 433.3 )
 
Not sure if theres a reg on it but it's fine to do that on a radial circuit as long as the protective device is the correct rating for the smaller cable, as you've done. What's the wattage of the oven? The cable might need to be changed if it needs to be on a 40 amp.
 
Not sure if theres a reg on it but it's fine to do that on a radial circuit as long as the protective device is the correct rating for the smaller cable, as you've done. What's the wattage of the oven? The cable might need to be changed if it needs to be on a 40 amp.
Total wattage 8215w. No socket at isolation switch. So with diversity 32A works.
 
No there isn't a reg requiring consistent cable throughout a circuit. (In fact 433.3 mentions the scenario of a reduction in CCC.)
If the 6 sq mm leg was clipped direct (when it can carry 47 amps before any further de-rating) it might have complied.

Basically 433.1.1 needs to be met for the whole circuit unless over-current protection can be legitimately omitted (see sections 433.2, 433.3 )
Thanks Tim. 👍🏼
 
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm. Does the cable have to be the same throughout? If so what is the reg for this please. 🤔

Why did you change the RCBO to 32A?

No there is no requirement for the same size cable to be used throughout as long as all cables used have adequate fault protection and, if required, overcurrent protection.
 
All seems a bit over the top to me and even if it were a technical regs breach you have to look at common sense. One of the first scenarios when I was in college doing the 2391 20 odd years ago was to calculate the cable size for an electric shower. following the regs to the letter it needed to be 25mm cable, the tutor said "obviously thats a load of -------s because it wont fit into the terminals so always us your common sense." Which has stuck with me ever since.

Only yesterday I wired a point for an oven that wasn't on site yet and some single ovens nowadays come with a plug so in this instance we wire a 6mm to an outlet plate and wire a single socket next to it in a dual box to give the appliance installer options. I only use a short length of 2.5 for the socket because, well, its just a single socket.
 

Reply to reg to say 2 different size cables cant be used on one circuit if rcbo rated to lower cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Got a house I am working in at moment, customer wants extra sockets downstairs, apart from kitchen the whole ground floor has just 3 double...
Replies
5
Views
2K
Hi all, need some opinions on the following please> Origin is a three phase 60A TN-C-S supply.it goes into a changeover switch (small PTO driven...
Replies
59
Views
6K
E
Hi Guys, Here We Go With Another Post That Causes Many Different Opinions On the Forum. Been asked to do the wiring for a new fitted kitchen in...
Replies
5
Views
4K
T
Hi, First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any...
Replies
24
Views
8K
Thai Amateur
T
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock