Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm. Does the cable have to be the same throughout? If so what is the reg for this please. 🤔
 
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm. Does the cable have to be the same throughout? If so what is the reg for this please. 🤔
No there isn't a reg requiring consistent cable throughout a circuit. (In fact 433.3 mentions the scenario of a reduction in CCC.)
If the 6 sq mm leg was clipped direct (when it can carry 47 amps before any further de-rating) it might have complied.

Basically 433.1.1 needs to be met for the whole circuit unless over-current protection can be legitimately omitted (see sections 433.2, 433.3 )
 
  • Agree
Reactions: pc1966
Not sure if theres a reg on it but it's fine to do that on a radial circuit as long as the protective device is the correct rating for the smaller cable, as you've done. What's the wattage of the oven? The cable might need to be changed if it needs to be on a 40 amp.
 
Not sure if theres a reg on it but it's fine to do that on a radial circuit as long as the protective device is the correct rating for the smaller cable, as you've done. What's the wattage of the oven? The cable might need to be changed if it needs to be on a 40 amp.
Total wattage 8215w. No socket at isolation switch. So with diversity 32A works.
 
No there isn't a reg requiring consistent cable throughout a circuit. (In fact 433.3 mentions the scenario of a reduction in CCC.)
If the 6 sq mm leg was clipped direct (when it can carry 47 amps before any further de-rating) it might have complied.

Basically 433.1.1 needs to be met for the whole circuit unless over-current protection can be legitimately omitted (see sections 433.2, 433.3 )
Thanks Tim. 👍🏼
 
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm. Does the cable have to be the same throughout? If so what is the reg for this please. 🤔

Why did you change the RCBO to 32A?

No there is no requirement for the same size cable to be used throughout as long as all cables used have adequate fault protection and, if required, overcurrent protection.
 
  • Agree
  • Like
Reactions: Risteard and pc1966
All seems a bit over the top to me and even if it were a technical regs breach you have to look at common sense. One of the first scenarios when I was in college doing the 2391 20 odd years ago was to calculate the cable size for an electric shower. following the regs to the letter it needed to be 25mm cable, the tutor said "obviously thats a load of -------s because it wont fit into the terminals so always us your common sense." Which has stuck with me ever since.

Only yesterday I wired a point for an oven that wasn't on site yet and some single ovens nowadays come with a plug so in this instance we wire a 6mm to an outlet plate and wire a single socket next to it in a dual box to give the appliance installer options. I only use a short length of 2.5 for the socket because, well, its just a single socket.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
reg to say 2 different size cables cant be used on one circuit if rcbo rated to lower cable?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Alexking1,
Last reply from
brianmoooore,
Replies
8
Views
2,699

Advert