Caravan, Static, whats the difference, if both are metal framed on Wheels or Bricks insulated from the ground then ESQCR requires thet the PME not to be connected.

Bare feet, metal frame at a different potential to true earth and then the added risk of a broken PEN.

TT unless you want to break thew LAW!
 
I'm pretty sure that there is a member here, that actually lives in one of these bigger mobile homes on a residental site, that is permanently connected to the mains power supply and that the supply was PME

There is nothing bare feet on metal in these units, normally fully carpeted or laminated throughout, most of them have decking around the place too!! ...lol!!! Some of these things are massive, totally uncomparable with your typical road and holiday caravans...:smiley2:
 
I'm pretty sure that there is a member here, that actually lives in one of these bigger mobile homes on a residental site, that is permanently connected to the mains power supply and that the supply was PME

There is nothing bare feet on metal in these units, normally fully carpeted or laminated throughout, most of them have decking around the place too!! ...lol!!! Some of these things are massive, totally uncomparable with your typical road and holiday caravans...:smiley2:

Lol, i was referring to bare feet outside not inside. The op is making refernece to Hook Up's, so not a permenant Fixed Electrical Installation, these Hook Up's pose a greater risk than a fixed sytem.

I agree some Residential Park Homes may not fall into the Caravan catorgory and have Fixed PME supplys, though this would be agreed through the DNO and the Manufactureres of the Homes(Some of which state there homes are suitable for PME).

For me what the OP is describing then TT is required and falls within ESQCR.
 
For me what the OP is describing then TT is required and falls within ESQCR
​


Agree, it just that the thread somehow got sidetracked away from the OP's original questions. I had already made my comments to these, in earlier posts..
 
To be fair in my ignorance ive never really read section717 as regards to static caravan's...

Suppose its up to the inspector at the time as to what regulation applys. Common sense required. Thanks for making me more aware of 717 though.

No worries fella, glad to be of help, and it is a grey area TBH, many interpretations can be assumed, as engineer points out some could be considered permanent, but not in this threads case IMO.
 
OK so I now have some more information about the supply characteristics as I got into the plant room today for a peep and I have some photo's of the existing installation which IMO leaves a lot to be desired.

It is a PME supply that has not been used for anything on the park as everything has been TT'd (mmmmm in a fashion) give me your opinions on what you see, there is only 1 earth rod that I can find that is at the origin (this has to be confirmed as there may be more in remote locations but not obvious) with runs of up to 100m using the SWA as the cpc that are not glanded correctly.

How do I upload photo's ?
 
127.jpgThis is the only earth rod that I could find on the site which is poorly installed at best.
125.jpgThis is the first in the line of 2 external distribution panels through the site that I could find
121.jpgThis is the only metering position that I could find at the site and the earth rod is installed behind this wall with the earth cable running up the side of the wooden back board straight from the rod to a mass joint behind the make shift enclosure above the isolation
 
whats the RA reading there? under 1667 perhaps or even under 200, it well maybe that one rod serves all TT supplies haha, it looks crap but it may be the case, I still recommend converting to tt at every 4 caravan plug points, can you confirm the supply at the distribution end is tn or tt?
 
whats the RA reading there? under 1667 perhaps or even under 200, it well maybe that one rod serves all TT supplies haha, it looks crap but it may be the case, I still recommend converting to tt at every 4 caravan plug points, can you confirm the supply at the distribution end is tn or tt?

Distribution end has a PME connection that has not been utilised as everything is TT using the 1 earth rod that I can locate and the RA is 57 ohms
 
well then providing the zs readings at the caravan sockets comply with the regs and section 7 details, not sure of what actual reg it is without looking there is no issue, seems fine to me, if you have the cable sizes worked out and rcd protection at the sockets and tt arrangments with zs readings within parameters then all fine IMO, I would prefer local earth rods myself, but hey if theres a rod and the readings are right I can't see a problem unless I'm missing something.
 
It appears that the SWA is used for the cpc to the external dist box and to he van hook ups, they are glanded but not earth link from banjo to an earth bar so it only takes 1 of these to come loose and if its the 1st 1 then the entire system has no earth.
 
Are there any permanent buildings on this caravan park, like a social club, shop, shower/toilet block etc?? If there is then these should be connected to the PME system, not connected to that single rod.

I can't make out head or tail of that external Distribution Panel, i hope you can make a better job of it than than that!! ...lol!! Couldn't see any flying earth leads off the SWA cables, unless they are located external, in fact couldn't see Any CPC within this panel at all!!

I wouldn't rely on that single earth rod system for all of the caravan parks hook-up pitches. As suggested earlier, at least one earth rod position for each leg supplying 4 pitches, that can be linked up back to the external distribution centre's and the main intake position via the SWA armouring and/or by a third core.


Are you sure the owners are going to stump up the money for all the changes?? I agree that as it stands now, the existing installation looks to be a pig's ear, designed and installed by Muppet's!! lol!!
 
Last edited by a moderator:
Are you sure the owners are going to stump up the money for all the changes?? I agree that as it stands now, the existing installation looks to be a pig's ear, designed and installed by Muppet's!! lol!!
AKA Kermit & Miss Piggy :)
 