Discuss Diversity for cooker in the regs? in the UK Electrical Forum area at ElectriciansForums.net
S
Spark2be
Can anyone tell me if it is a regulation required to apply diversity when designing a cooker circuit?
Before anyone asks I start my 17th edition course in September.
it says you CAN apply diversity...not that you MUST....as long as the Ib is less than the In....and the Iz is equal or greater than the In....then its good to go
definitely. as it means you can reduce the cost of the cable used.
yes .........................to be honest I doubt if there is a single installation in the UK that is not designed with a degree of diversity involved ...............well any proper installation will be
I agree with camelchops
if diversity were not used then every house would need a 300amp supply!
Diversity is not an exact science, however. It is something that is done as part of the design of an installation and it's up to the designer to use his experience to make the appropriate allowances.
The diversity figures in the On Site Guide are a good starting point, but please note the word GUIDE!!
Reply to Diversity for cooker in the regs? in the UK Electrical Forum area at ElectriciansForums.net
Hello Guys Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven. I've looked at...
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...