Try reading #5, maybe?agreed on the RCD, but he’s not told us about the correct fuse. !

Try reading #5, maybe?agreed on the RCD, but he’s not told us about the correct fuse. !

Why? It’s only feeding a twin socket so maximum it’s going to pull is 26A. Clipped direct it’s rated at 27APull that fuse out now!
Your 2.5 is only rated at 24A.
Fuses aren't just for overload protection, though....and who knows the state of the cable and socket.Why? It’s only feeding a twin socket so maximum it’s going to pull is 26A. Clipped direct it’s rated at 27A
I know, but saying the cable will be overloaded is incorrect, unless he’s plugging in something that’s not designed for a 13A plug top.Fuses aren't just for overload protection, though.
What if there's a circuit fault.......many a burnt up cable as a result. It's probably OK but who knows?I know, but saying the cable will be overloaded is incorrect, unless he’s plugging in something that’s not designed for a 13A plug top.
I did say assuming correct fuse and now it seems it is the 45A.You’ve looked at the right hand fuse. That is usually a 45A fuse, so ignore the above.
show us a photo of under the left hand fuse cover. It will be one of these that controls the garage circuit. Tell us which of the fuses it is.
[automerge]1598288374[/automerge]
agreed on the RCD, but he’s not told us about the correct fuse. !
I’m not saying it’s right, I’m only questioning him saying it needs removing immediately which I disagree with.What if there's a circuit fault.......many a burnt up cable as a result. It's probably OK but who knows?
Oh stupid meTry reading #5, maybe?![]()
There is nothing between where the cable becomes visible (from behind the fuse box) and the socket. We have a gas cooker so I can't say but nothing in the house nor the garage lights are affected only the double socket.Oh stupid me
[automerge]1598293185[/automerge]
@alljohn just a thought
when you remove the 45A fuse, is the garage the only thing that turns off?
What happens to the cooker?
When the cable comes in to the garage, does it go straight to the socket, or us there anything else connected before the socket?
It would be for the existing double socket (i.e. no additional sockets).Is that fuse just for your sockets, or is it somehow feeding other stuff?
Looking at it from the outside, the new socket project has the look of a slow car-crash and really needs someone competent to take a closer look and check that the various fundamental safety aspects are really being met.
I'm wanting to add extra sockets