Fuses aren't just for overload protection, though.
I know, but saying the cable will be overloaded is incorrect, unless he’s plugging in something that’s not designed for a 13A plug top.
 
You’ve looked at the right hand fuse. That is usually a 45A fuse, so ignore the above.
show us a photo of under the left hand fuse cover. It will be one of these that controls the garage circuit. Tell us which of the fuses it is.
[automerge]1598288374[/automerge]


agreed on the RCD, but he’s not told us about the correct fuse. !
I did say assuming correct fuse and now it seems it is the 45A.
 
Try reading #5, maybe? ;)
Oh stupid me :flushed::flushed:
[automerge]1598293185[/automerge]
@alljohn just a thought

when you remove the 45A fuse, is the garage the only thing that turns off?
What happens to the cooker?

When the cable comes in to the garage, does it go straight to the socket, or us there anything else connected before the socket?
 
Last edited:
Oh stupid me :flushed::flushed:
[automerge]1598293185[/automerge]
@alljohn just a thought

when you remove the 45A fuse, is the garage the only thing that turns off?
What happens to the cooker?

When the cable comes in to the garage, does it go straight to the socket, or us there anything else connected before the socket?
There is nothing between where the cable becomes visible (from behind the fuse box) and the socket. We have a gas cooker so I can't say but nothing in the house nor the garage lights are affected only the double socket.
Thanks
 
Ok. Your basic problem is that sockets, particularly additional sockets must be RCD protected. Your elderly fuse board has no RCD protection.
There is a way to do this, but you need a competent electrician to do this.

Your secondary problem is the fuse size. It’s too big for that single smallish cable. It’s tolerable because you only have a double socket on the end. Add more sockets and tthe cable could exceed its maximum current ceiling. The cable might overheat, and you don’t want that to happen. The circuit needs sorting out and the correct fuse used according to your expected load and the size of the cable. Again, this is a job for
a competent electrician.
 
Is that fuse just for your sockets, or is it somehow feeding other stuff?

Looking at it from the outside, the new socket project has the look of a slow car-crash and really needs someone competent to take a closer look and check that the various fundamental safety aspects are really being met.
 
Is that fuse just for your sockets, or is it somehow feeding other stuff?

Looking at it from the outside, the new socket project has the look of a slow car-crash and really needs someone competent to take a closer look and check that the various fundamental safety aspects are really being met.
It would be for the existing double socket (i.e. no additional sockets).
 