I've been asked to install a power supply for a sun bed in a salon:
Sunbed is 60 x 225w lamps = 13.5K
Divide 230v = 59amps
Table 4D2A:
10mm T&E 63amp capacity clipped direct.
I'm installing a dedicated CU with a 63a MCB and isolator fed via a henley block on the meter tails for the sunbed to avoid the basement studio being plunged into darkness!
So far so good.
I haven't got paperwork for the sunbed but I understand that the ballasts typically have an earth leakage current of 75ma which increases over time. So 30ma RCDs can't be used. 100ma are not recommended for shock protection.

Am I required to protect this circuit with an RCD?

Thanks
Steve
 
IMO, an RCD is not required as long as the cable is not buried in a wall <50mm deep. however, i'd be measuring Ze and calculating Zs and PEFC to ensure that the cpc in 10mm T/E was adequate.
 
Thanks for the quick responses, much appreciated.
The manufacturer, Sunquest's (Aurora) website has very basic information unfortunately.
Client bought the most powerful model before taking advice on the power requirements of course. Luckily only a 3 metre run to the board.
2 guys coming down from Leicester crack of sparrow f**t to install expecting everything to be ready...
Regards
Steve
 
開溜所有,它是在中國,所以草皮吧。
 
All installed now.
Blokes who installed it both had tanning parlours in Leicester. They reckoned just a couple of vents needed. No fan. Cabinets are used 6 mins at a time.
See how it goes, not the easiest place to install a ventilation duct.
Cheers Steve
 
All installed now.
Blokes who installed it both had tanning parlours in Leicester. They reckoned just a couple of vents needed. No fan. Cabinets are used 6 mins at a time.
See how it goes, not the easiest place to install a ventilation duct.
Cheers Steve

Qualified for the job then lol. Did you end up sticking it on a RCD?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
West London

Thread Information

Title
Does a sunbed require RCD?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Stevesplatto,
Last reply from
Simlec,
Replies
17
Views
13,158

Advert

Back
Top