FBA1B49B-2CB6-4EA4-A9BE-5B232A320243.jpeg Hi everyone. I’ve been asked to quote for a repossessed property that needs a consumer unit change. The incoming supply configuration is as shown in the image. As the tails come straight of the suppliers meter what is the correct way to approach changing the tails. Do I need to contact the supplier? Thanks
 
Depends who the energy supplier or dno is for this property. Some suppliers will do install an isolator free.or quite cheaply. Where as dnos vary quite a bit
Western power distributiom charge 75 inc vat to pull a fuse. And wait 1 hour whilst you fit an isolator yourself. Otherwise its another 75 to put fuse in. I always have isolator and new tails on wall ready to go.
SSE allow you if in a scheme to pull the fuse on single phase domestic properties. In anycase if its old and especially if a metal cutout leave well alone. Easily brake or arc. The dno wont pull a fuse out a metal cut out around here due to risks.
If its a nice new modern henley cutout then i gather the seal fairies like to visit these.
 
exend the tails if required.
considering their is a tele switch his it a flat a house or a barn.
It’s a rather large old house. Been vacant for 6-8 years. Was Eon supply but the tenant ran a high amount of debt before leaving. The new owners are switching supply to Bulb. Can the tele switch be removed in this instance? Maybe the correct approach is to ask the new owners if they have a dual tariff arrangement. Thank you
 
The new owners must have the new isolator installed before any work is carried out , considering you are qouting for the job .
i would not give to much infomation before you get the job ,if you know what i mean.
 
I assume the off peak loads controlled by the teleswitch are now gone, I see no connection to the switched output terminals. Might be worth changing to a normal rate supply at the same time if this is the case.
 

Reply to Domestic installation advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
777
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K
DNO ripped out antique main incomer/breaker .The guy hated us and himself and everyone else by the end of the job ! . Client going to contact...
Replies
21
Views
2K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock