Is having all the lighting circuits on 1 RCD in a dual board considered a C3 on an EICR? To me it defeats the object of the exercise.
 
Is having all the lighting circuits on 1 RCD in a dual board considered a C3 on an EICR? To me it defeats the object of the exercise.
what do you think about the fact for a small cost to the customer you could swap one circuit over to the other RCD and not make mountains out of mole hills?
 
what do you think about the fact for a small cost to the customer you could swap one circuit over to the other RCD and not make mountains out of mole hills?
The occupier of the house is moving so he dosent care, if new owners want it done if and when they complete the house sale I shall oblige.
 
That's what Mods do, hang on----------he isn't is he, hmm, maybe after 50,000 posts he may get promoted LOL
 
Is having all the lighting circuits on 1 RCD in a dual board considered a C3 on an EICR? To me it defeats the object of the exercise.

Could it be that there is only 1 socket circuit?? and that's why it was done!

Need more information.

For what its worth I wouldn't even code it.
 
what do you think about the fact for a small cost to the customer you could swap one circuit over to the other RCD and not make mountains out of mole hills?
depends Mike....
its probably got a shared neutral in there and if its a tw&t to run.....as some of em can be....epecially if old Mrs. Brady dont want her decor damaging in any way...
 
if there was a shared neutral, then i'd give it a code C3. mybe if i was in a bad mood, like if the offy had run out of beer, then a C2. after all, if a Electrical Trainee isolates the upstairs lights to change the landing lights, it's a potential danger. on 2nd thoughts, bugger it. 1 down 55,999 to go.
 
if there was a shared neutral, then i'd give it a code C3. mybe if i was in a bad mood, like if the offy had run out of beer, then a C2. after all, if a Electrical Trainee isolates the upstairs lights to change the landing lights, it's a potential danger. on 2nd thoughts, bugger it. 1 down 55,999 to go.
thats why both lighting circuits go on the same OPD Tel in them situations.....
 