Evening all, new to the forum.
I have a question regarding the location of the earth bonding clamp on a gas meter, I know it is supposed to be within 600mm of the gas meter but the problem is the CU is located in the kitchen in the rear of the property and the GM is located diagonally opposite on the front of the property.
The combi boiler is also in the kitchen, so my question is can I bond at the boiler or will I have to run the earth cable around the property
It's not possible to run the cable through the property as the home owner won't allow me to due to the fact that it has recently been decorated .
Thanks in advance Marmalade.
 
Aico 3000
Scolmore Electrical Products
This official sponsor may provide discounts for members
D

Dustydazzler

-
Esteemed
Arms
600mm from where the pipe enters the property / where practically possible

my gut feeling is you should run the cable round to the meter Position
 
R

radiohead

Esteemed
Arms
It should be at the point of entry, but have you ascertained it requires main bonding? It may be a plastic service pipe.
 
Dave OCD

Dave OCD

-
Mentor
Esteemed
Arms
If it does need bonding and is a real pain to get to the other end of the house I can't see any harm in connecting the main gas bond at the boiler. But I'd note this on the certificate with the reason.
 
M

Marmalade

  • Thread Starter Thread Starter
  • #5
It should be at the point of entry, but have you ascertained it requires main bonding? It may be a plastic service pipe.
I'm sure it's copper but I will double check
Post automatically merged:

600mm from where the pipe enters the property / where practically possible

my gut feeling is you should run the cable round to the mete
If it does need bonding and is a real pain to get to the other end of the house I can't see any harm in connecting the main gas bond at the boiler. But I'd note this on the certificate with the reason.
That was my thinking but its always better to have a second opinion .
 
Last edited:
P

pc1966

Esteemed
Arms
Supporter
Are there any other gas appliances?

If there is only the boiler and you plan on bonding at the gas pipe there then at the very least you ought to use a wander lead and verify that the gas pipe work is properly connected (electrically speaking) or completely isolated (unlikely as I don't think you ever see non-metal pipe in domestic gas) between the meter outlet pipe and the appliance.
 
M

Marmalade

  • Thread Starter Thread Starter
  • #7
Thank you all for your thoughts on this problem.
👍
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
I'm sure it's copper but I will double check
That is unlikely, copper is rarely, if ever, used on the supply side of a gas meter. Normally it will be screwed iron pipe (older supplies) or MDPE (newer supplies)

Either way you should test to establish whether or not it is extraneous regardless of what the incoming pipe is made of.
 
Wilko

Wilko

-
Esteemed
Arms
as I don't think you ever see non-metal pipe in domestic gas
Hi - agreed, after the meter a flex pipe can be used as final connection to a moveable cooker for example, but that’s it AFAIK.
 
Mike Johnson

Mike Johnson

-
Esteemed
Arms
I was going to post that I doubt the supply into the property is copper, but Dave beat me too it, Oh damm now I have posted it.
 