I like to think so, I'm still learning everyday day. I've only been on my own for a few months but have been on the tools for 8 years.

I find with this game you only know what you've come across before.
 
As you have a screwed thread on that conduit, you could use a ''Piranha'' earthing nut on the ends of that conduit. You'll achieve a far better earthing connection than the present strap you have now.
You may need to cut a little off the couplings though, to make room for the earthing nut.
 
Think a point is being missed here years ago people did not run earths as the containment system ie conduit trunking was and is known as Electrically & Mechanically sound. You have a conduit distribution system for mechanical protection as well as being you main source for an earth and it is common in blocks of flats and terraced houses.

Now after say that and please do not take this the wrong way you went to see the job without your tester then posted a question here causing a lot of speculation if there is one thing you need to learn is take the tester do your Ze PFC,PSSC and a global IR test then ask your question remember to ignore the bit of 6 mm coming of the earth strap on the conduit and just measure the Ze on the conduit why because if doing a CU change you will be upgrading this plus the earth lead
 
I would usually take a tester to a job but I was out in the car, not in my van when I got the chance to pop over. Was quite late in the eve but the guys gone away for a week so I needed to see him.

Arranged for the maintenance to open up the main cupboard tomorrow so I can check it out.

Have some led feature lighting, and a few other bits to sort while I wait for them.

I bet it'll snow and they won't turn up. Lol

I understand the containment earthing, but I didn't know IF I was complying with regs by using it.

Thanks eng59 that's a good idea.
 
0.09 ze

Conduits for all the flats run to a gland plate which is bonded to a MET from that to the sheath TN-S
 