Ah, but you could easily obtain a decent level of stability and with it, much lower Ra value too boot!! Which is and has been the whole essence of my position throughout...

I always get a stable result no matter what the Ra value. 2 x 1200 x 5/8" rods is standard for me. If I get 20 ohms (HIGHLY unlikely) happy days, if I get 150-250 ohms, (more likely) happy days. The result makes no odds to me. The last and only install I left over 200 ohms I checked quarterly for a year (I'll admit, I WAS worried at one point) but there was absolutely no variation on the readings.

You have to bear in mind that most of where I live is about 18"-24" of top soil then straight into solid chalk. Absolute CRAP for any sort of decent TT system! Hence why the typical domestic I spec always includes type-s RCDs.

The more agricultural TTs round here 'tend' to be more in land, so better ground conditions and a much higher chance of achieving a TN value.
 
I always get a stable result no matter what the Ra value. 2 x 1200 x 5/8" rods is standard for me. If I get 20 ohms (HIGHLY unlikely) happy days, if I get 150-250 ohms, (more likely) happy days. The result makes no odds to me. The last and only install I left over 200 ohms I checked quarterly for a year (I'll admit, I WAS worried at one point) but there was absolutely no variation on the readings.

You have to bear in mind that most of where I live is about 18"-24" of top soil then straight into solid chalk. Absolute CRAP for any sort of decent TT system! Hence why the typical domestic I spec always includes type-s RCDs.

The more agricultural TTs round here 'tend' to be more in land, so better ground conditions and a much higher chance of achieving a TN value.

Is this because you cannot get a rod into the chalk or do you feel that it's electrical properties prevent a lower reading?
 
Getting two rods into chalk, although a sweaty task has never been the problem. The problem is that chalk when not soaked isn't really known for its fantastic conducting properties.

P.s. I appreciate the apology.
 
Getting two rods into chalk, although a sweaty task has never been the problem. The problem is that chalk when not soaked isn't really known for its fantastic conducting properties.

Actually calcium carbonate has reasonable electrical properties, of course better when full of the wet stuff, but within about 50m of the surface the chalk will have enough moisture in it naturally to assist in getting a better reading than you may think. I appreciate that there will be differences with location and that the permittivity of the chalk will always be a restricting factor compared to a peat or clay based soil, but you would be surprised how low you can get it even you might think the chalk is dry...the real problem is if you happen to hit a quartz or flint inclusion into the rock, or if your more toward the south west (I know you personally are not) then you can get basaltic inclusions into the chalk..which whilst having excellent permittivity is a real biatch to drive a rod into :)



P.s. I appreciate the apology.

Despite how I might seem sometimes, I do not set out to offend and will always apologise if I feel I have either offended or simply overstepped the mark
 
Actually calcium carbonate has reasonable electrical properties, of course better when full of the wet stuff, but within about 50m of the surface the chalk will have enough moisture in it naturally to assist in getting a better reading than you may think. I appreciate that there will be differences with location and that the permittivity of the chalk will always be a restricting factor compared to a peat or clay based soil, but you would be surprised how low you can get it even you might think the chalk is dry...the real problem is if you happen to hit a quartz or flint inclusion into the rock, or if your more toward the south west (I know you personally are not) then you can get basaltic inclusions into the chalk..which whilst having excellent permittivity is a real biatch to drive a rod into :)





Despite how I might seem sometimes, I do not set out to offend and will always apologise if I feel I have either offended or simply overstepped the mark

i sometimes do though...
 
The problem is that water here tends to just sit on the chalk it is so thick set which is why we have such soggy ground. My experience of driving rods into south east coast chalk is that you end up with much higher values than soil, clay or loose lay chalk found towards the south west. Like I said, with 2400mm worth of copper I can almost guarantee a reading higher than 150ohms, in fact, I'd bet money on it. It just isn't economically viable to try and get lower values down here. As long as the value obtained is stable, RCDs are the only way.

The best values I have ever obtained on TT systems have always been in the clay bed about 20 miles in land.
 
The problem is that water here tends to just sit on the chalk it is so thick set which is why we have such soggy ground. My experience of driving rods into south east coast chalk is that you end up with much higher values than soil, clay or loose lay chalk found towards the south west. Like I said, with 2400mm worth of copper I can almost guarantee a reading higher than 150ohms, in fact, I'd bet money on it. It just isn't economically viable to try and get lower values down here. As long as the value obtained is stable, RCDs are the only way.

The best values I have ever obtained on TT systems have always been in the clay bed about 20 miles in land.

Which is where I am...a recent TT with two 5/8 coupled rods as a replacement for an existing 700 ohm reading got 12 ohms.Some would argue I should have gone on,I would refer them to post 70!
 
Apologies if I have missed something, but I've often wondered what is the point of trying to achieve TN figures when the distributor's earth electrode at the supply transformer could be as high as 21 ohms (usual stated maximum)?
 
I was rather enjoying the debate with Eng, now I can't be bothered.
Thanks to everyone for toning it down a bit, much appreciated. This is always an emotive issue but I also enjoy the debate and I also think it's a worthy topic.

I'll have to accept your argument there as such things are outside of my experience. Can I ask if you have any evidence of actual situations where a high Ra has contributed to the scenario you describe?
Please don't think I'm some kind of earthing expert because I'm not, there's others on this thread who probably have far more experience and theory than me. I've had two separate HVACR plant manufactures failure reports in the past, different sites, different manufacturers and years apart. Both failures were due to corrosion and both occasions convincing evidence was presented proving it was due to various earthing issues but high impedance was the main contributing factor.

This topic has always polarised opinion and ended in tears....no need to get antagonistic matey,but apologies if your thread has been hijacked somewhat!
Yeah, I'm afraid this has gone somewhat off-topic from your original question Justin, apologies for that. Hopefully your original question was answered with enough info for you to decide.

no-one is ever going to go to the effort of trying to get sub 10 ohm readings for a domestic TT
its just not cost effective for the deminishing improvements that it brings for the average home-owner.
engineering practice takes back seat to value for money in the domestic market , simple econonmics im afraid.
I think this is a big part of the problem. By allowing a rediculously high Ra in the regs it means that there's no motivation for installers to even attempt to get better readings. In fact those who are conscientious about getting the lowest Ra possible will actually be pricing themselves out of the work so the regs could actually be a deterrent to good practice.
 
1ohm? Get off lol


It's not always as difficult as you may think. You will know, or should i say a good indication as to if the possibility is there, is from the values obtained after driving in 2 X 5/8'' rods. Again this will obviously depend on soil/ground make-up, but in general terms it can be achieved, or very close to it!!

I know several areas/villages in Essex where you would have no problem obtaining better TT values with just two rods or one 2.4m rod, (and as stable as a rock) than those in near-by towns with DNO TN-S (or was) earth provision, ...i jest not!! lol!!



quote_icon.png
Originally Posted by D Skelton You have to bear in mind that most of where I live is about 18"-24" of top soil then straight into solid chalk. Absolute CRAP for any sort of decent TT system! Hence why the typical domestic I spec always includes type-s RCDs.

I have no problem at all with what you have said here, There are always going to be situations where the conditions you are facing makes little sense financially, to continue past a reasonable point.
 
i've done hundreds of earth rod installs ( no exaguration ) whilst working for a county council highways dept.
we had entire roadworks teams with mini diggers and pneumatic jack hammers to install these earth rod installations at the end of every principle street lighting network.
our goal , set by the client engineer , was 20 ohms , a good solid & stable figure in my opinion.
99% of the time we achieved it , but sometimes with extra rods , sometimes by abandoning one location and trying another spot.
i can count on 1 hand the number of times we got less than 8 ohms.
so anyone insisting that a 1 ohm reading is realistic target for a domestic TT is clearly talking out of their arse.
;-)

I can understand those figures if were talking about highway lighting and the like!! Why they don't install the earth rods prior to the sometimes very deep stoned hardcore bases i don't know. It's what we do on any on-site roads, and our bases are no-where near the depth of some of the motorway bases i've seen, ...notably the M2 upgrades in Kent.
 
It's not always as difficult as you may think. You will know, or should i say a good indication as to if the possibility is there, is from the values obtained after driving in 2 X 5/8'' rods. Again this will obviously depend on soil/ground make-up, but in general terms it can be achieved, or very close to it!!

I know several areas/villages in Essex where you would have no problem obtaining better TT values with just two rods or one 2.4m rod, (and as stable as a rock) than those in near-by towns with DNO TN-S (or was) earth provision, ...i jest not!! lol!!





I have no problem at all with what you have said here, There are always going to be situations where the conditions you are facing makes little sense financially, to continue past a reasonable point.
Appreciate that fella, I have had readings of around 3 ohms before, around here with the Cotswold stone in the ground 20-30 is the norm with 2 5ft rods screwed together though.
 
Sorry chaps, but STILL no-one has actually answered my point from earlier:

If we've got a typical BS-EN60898 distribution environment, and 245V as our actual incoming voltage, what the heck difference does it make to our disconnection times being met (or not) as to whether we've got 20 ohms or 200 ohms - each is no good!

Agreed, if we can attain 1, 2 or maybe 3 ohms then we stand a chance, but anything else it's just not a logical issue.

And I also think that people need to take a reality check about the domestic market place - Mrs Jones is just NOT going to either appreciate nor pay for a gang of blokes to make a mess of her garden/drive/patio whatever and charge her a fortune for it either, irrespective of the electrical ideals involved.
 
Sorry chaps, but STILL no-one has actually answered my point from earlier:

If we've got a typical BS-EN60898 distribution environment, and 245V as our actual incoming voltage, what the heck difference does it make to our disconnection times being met (or not) as to whether we've got 20 ohms or 200 ohms - each is no good!

Agreed, if we can attain 1, 2 or maybe 3 ohms then we stand a chance, but anything else it's just not a logical issue.

And I also think that people need to take a reality check about the domestic market place - Mrs Jones is just NOT going to either appreciate nor pay for a gang of blokes to make a mess of her garden/drive/patio whatever and charge her a fortune for it either, irrespective of the electrical ideals involved.

Welcome to the 'It doesnt make sense whatever they say' club Matey!....Think there may be as many as 3 or 4 of us in it now?
 
Sorry chaps, but STILL no-one has actually answered my point from earlier

I keep asking people to prove the existence of God. I know full well that there is no such thing. I make very clear that reason and logic is what leads me to believe that the existence of God is highly improbable, but that still won't stop billions of people world wide believing in some sort of deity.

I think we're past the point of resolution, you just have to accept as I have that they believe what they believe and we believe what we believe. We're right of course ;) hahaha, but they will never see it.
 