Not sure what your saying here, if an installation ''requires'' a TT system to be installed, then your going to have to make a mess of Mrs Jones dahlias anyway, if that's the only place to drive your rods.
No-ones making grand statements either, i've made the point several, several times over, that any typical domestic house TT system, should be a minimum of 2 X 5/8'' rods or preferably a single 2.4m 5/8'' rod. Are you saying this is OTT??
No, I'm not saying that is OTT at all - in fact I quite agree - what I am saying is that there is a point of diminishing return and assertions of being able to achieve TN figures de facto just don't stack up in real life. Hence....we end up falling back on our RCD as primary not secondary protection - and in which case - we end up full circle back with what does it therefore matter if I've got 10 or 100 ohms, both are equally useless.