The problem is that water here tends to just sit on the chalk it is so thick set which is why we have such soggy ground. My experience of driving rods into south east coast chalk is that you end up with much higher values than soil, clay or loose lay chalk found towards the south west. Like I said, with 2400mm worth of copper I can almost guarantee a reading higher than 150ohms, in fact, I'd bet money on it. It just isn't economically viable to try and get lower values down here. As long as the value obtained is stable, RCDs are the only way.
The best values I have ever obtained on TT systems have always been in the clay bed about 20 miles in land.