Sorry chaps, but STILL no-one has actually answered my point from earlier:

If we've got a typical BS-EN60898 distribution environment, and 245V as our actual incoming voltage, what the heck difference does it make to our disconnection times being met (or not) as to whether we've got 20 ohms or 200 ohms - each is no good!

Agreed, if we can attain 1, 2 or maybe 3 ohms then we stand a chance, but anything else it's just not a logical issue.

And I also think that people need to take a reality check about the domestic market place - Mrs Jones is just NOT going to either appreciate nor pay for a gang of blokes to make a mess of her garden/drive/patio whatever and charge her a fortune for it either, irrespective of the electrical ideals involved.

Perhaps if you read Marvo's posts # 55/57 you will see that's not quite the case at all, it's NOT all about disconnection times. These are points i brought up many many threads ago, maybe 18 months ago or more, but as always were poo, pooed by the one track mind brigade. This time, they seemed to have agreed on the argument (well for a few hours anyway), but have sadly fallen back to the crap given in the good old BS7671 along with, it doesn't matter if you attain 20 ohms or 200 ohms!! Well as the old saying goes you can lead the horse to water, but....


Where pray, has anyone suggested anything of the sort, about gangs of guy's and digging up gardens, drives and patio's?? This is just pure OTT nonsense, designed to substantiate a stand on a position that is fast crumbling under your feet!! And probably the reason why, they're only 3 or 4 of you!!
 
Sorry Eng, you've lost me now. If its NOT all about disconnection times, in an ADS design, then what IS it about?! I understand completely the inadequacies of BS7671 in certain areas, some of us have to work with the damn thing day in and out, but if we're now going so off piste as to start dismissing dis times, secondary protection and Ra values then please someone shoot me now!

I understand Marvo's comments about functionality, but logic would suggest that if you get the rare event of high standing current throughs SMPs / whatever then as your socket outlet is 30mA RCD protected regardless, even if you have an Ra of .01 the final cct RCD is going to break regardless, so it actually doesn't matter how efficient the conductivity.

And the practical reality of Mrs Jones garden isn't all that removed from my hammed-up version....you go 1 to 2m away from footings to sink a rod and you're in the middle of someone's lawn!!
 
Last edited:
Sorry Eng, you've lost me now. If its NOT all about disconnection times, in an ADS design, then what IS it about?! I understand completely the inadequacies of BS7671 in certain areas, some of us have to work with the damn thing day in and out, but if we're now going so off piste as to start dismissing dis times, secondary protection and Ra values then please someone shoot me now!

And the practical reality of Mrs Jones garden isn't all that removed from my hammed-up version....you go 1 to 2m away from footings to sink a rod and you're in the middle of someone's lawn!!
who said owt about someones lawn eh?
get a grip will ya....
 
who said owt about someones lawn eh?
get a grip will ya....

My grip is firmly where it ought to be! ;). My point is that if you draw a 1m boundary around the vast majority of domestic properties you will find an awful lot of places that no-one would want to sink a rod, cover, cable etc.
 
As i pointed out above, read Marvo's posts, he has given viable and factual reasons, to keep TT impedance's as low as reasonably possible.

I'll state again, if you consider 2 X 5/8'' rods as being the standard minimum size and depth for any domestic TT installation, your not going to go far wrong in the majority of situations in the UK. Though i can't see as an extra rod is going to be OTT on costs if your original Ra value, indicates that a very low single digit value will be achieved by doing so!!

You are going to have go to into someone lawn or whatever, no matter how many rods you may or may not install. That's the nature of any TT install.
 
Perhaps if you read Marvo's posts # 55/57 you will see that's not quite the case at all, it's NOT all about disconnection times. These are points i brought up many many threads ago, maybe 18 months ago or more, but as always were poo, pooed by the one track mind brigade. This time, they seemed to have agreed on the argument (well for a few hours anyway), but have sadly fallen back to the crap given in the good old BS7671 along with, it doesn't matter if you attain 20 ohms or 200 ohms!! Well as the old saying goes you can lead the horse to water, but....


Where pray, has anyone suggested anything of the sort, about gangs of guy's and digging up gardens, drives and patio's?? This is just pure OTT nonsense, designed to substantiate a stand on a position that is fast crumbling under your feet!! And probably the reason why, they're only 3 or 4 of you!!

Because having thought about Marvo's comments on reasons other than disconnection times for an Ra value I am convinced that such things are not relevant to the small scale TT installs I and most others work on. I am also convinced that if the potential issues Marvo highlighted were realistic the IEE would have been on it way before now,they hardly need any excuse to bring out an ammendment and fill their coffers.
 
Rockingit;787202[COLOR=#ff0000 said:
]My grip is firmly where it ought to be![/COLOR] ;). My point is that if you draw a 1m boundary around the vast majority of domestic properties you will find an awful lot of places that no-one would want to sink a rod, cover, cable etc.
lol....
we dont need toooo much info on a pubic forum rockin.....
 
My grip is firmly where it ought to be! ;). My point is that if you draw a 1m boundary around the vast majority of domestic properties you will find an awful lot of places that no-one would want to sink a rod, cover, cable etc.

As i say, if the property needs a TT system installing, it has to go in somewhere no matter how many rods you intend to sink!! That's a bit of a non-starter, as far as the prevailing discussion is concerned...
 
As i say, if the property needs a TT system installing, it has to go in somewhere no matter how many rods you intend to sink!! That's a bit of a non-starter, as far as the prevailing discussion is concerned...

Well, that's agreed here, too, as far as logical arguments is concerned. All I was trying to hammer home was the point of how, whether we like it or not, in the domestic environment (which is the majority of this forum) the same practical rules just don't exist as for an industrial/commercial job. It's fine and dandy to be able to make grand statements about being able to achieve TN values when you have the resources, and budget, available to make it happen. When Sparky X has spent an hour trampling down the dahlias whilst banging two rods down at £25-30 /hr, plus £20+ on bits, Mrs Jones is tapping her feet and looking at the bill wondering what on earth does this have to do with the new light she's asked to be fitted in the front room.
 
Not sure what your saying here, if an installation ''requires'' a TT system to be installed, then your going to have to make a mess of Mrs Jones dahlias anyway, if that's the only place to drive your rods.

No-ones making grand statements either, i've made the point several, several times over, that any typical domestic house TT system, should be a minimum of 2 X 5/8'' rods or preferably a single 2.4m 5/8'' rod. Are you saying this is OTT??
 
Not sure what your saying here, if an installation ''requires'' a TT system to be installed, then your going to have to make a mess of Mrs Jones dahlias anyway, if that's the only place to drive your rods.

No-ones making grand statements either, i've made the point several, several times over, that any typical domestic house TT system, should be a minimum of 2 X 5/8'' rods or preferably a single 2.4m 5/8'' rod. Are you saying this is OTT??

No, I'm not saying that is OTT at all - in fact I quite agree - what I am saying is that there is a point of diminishing return and assertions of being able to achieve TN figures de facto just don't stack up in real life. Hence....we end up falling back on our RCD as primary not secondary protection - and in which case - we end up full circle back with what does it therefore matter if I've got 10 or 100 ohms, both are equally useless.
 
Because having thought about Marvo's comments on reasons other than disconnection times for an Ra value I am convinced that such things are not relevant to the small scale TT installs I and most others work on. I am also convinced that if the potential issues Marvo highlighted were realistic the IEE would have been on it way before now,they hardly need any excuse to bring out an ammendment and fill their coffers.

Well, ...if were talking about a garden shed or garage with a light and a socket, you'd probably be somewhere near right. As far as a TT system for a complete house, i'd be taking a good deal more care!! We often never consider, that a TT system will be in place and serving that domestic installation for 30 years and more often than not, a good deal longer...

As far as the IET position goes, they don't seem to worry much too about the many contradictions contained in the BGB and the OSG's etc. Plenty of room for improvement and filling their coffers there alone!! A complete revision of the TT section wouldn't go amiss either!!
 
Last edited by a moderator:
No, I'm not saying that is OTT at all - in fact I quite agree - what I am saying is that there is a point of diminishing return and assertions of being able to achieve TN figures de facto just don't stack up in real life. Hence....we end up falling back on our RCD as primary not secondary protection - and in which case - we end up full circle back with what does it therefore matter if I've got 10 or 100 ohms, both are equally useless.

I give up!!
 
I give up!!

LOL! I know the feeling!! SO...please explain to me, in specific blow by blow detail so that there is no ambiguity to dispute:

Scenario;
a) TT, BS88:2 @ 80A
b) Incoming services all plastic
c) measured U of 245V
d) Resistive load on dedicated radial, B32, R1R2 value of 0.3 ohms
e) load becomes fault, direct R1>R2

Applying the general rules for ADS,
1) what is the outcome with an Ra at 20 ohms?
2) what is the outcome with an Ra at 200 ohms?
 