How so? They both achieve exactly the same thing!
What makes people look daft to me is when they say a stable 10/20/30/40ohms is better than a stable 200ohms. Your 40ohms is just as useless as 200 of them!!!
WTF..did you read my posts FFS, Posts like that make you look a dick.
A resistance of 10Ω is clearly not doing the same as a resistance of 200Ω because the fault current will be higher (Do the ruddy maths and it will prove it)...now as I said in my posts you failed to read
I did not say that this was an acceptable reading FFS, so take the earth rod out of your arse, remove the mega and PLEASE read what is said and not what you want it to say so you are all big and winning an argument..when we were not having one in the first place.
If you want my opinion on this, which I have refrained from giving in this thread then it is this...
BSI and the IET committee were wrong to state a 200Ω figure, it should have been 2Ω as a maximum for earth rods. However in my humble opinion any spark who does not achieve a reading, without good reason, of a maximum of 1Ω is failing in their moral responsibility to ensure that all fault currents are cleared effectively and disconnection times will always be compliant no matter what happens to the ground.
Pushing 4 or 5 rods into the ground is not real different from 2 rods, the regulations do not require a single earthing point, only that the earth paths do not overlap for adjacent rods.
I personally have driven five stacks of 4 rods into the ground around a structure to ensure that not only did it have adequate lightning protection but that the Zs reading was around 0.6Ω, and this was stable over many years.
If you investigate and price a job correctly then you should take into account the need to multiple rods, realistically a stack of 3 or 4 rods should meet the needs of the majority of installations to achieve a sub 1Ω Zs, but there is always an exception to the norm.