but to state lower values are not better is a statement that has the potential of making you look daft.

How so? They both achieve exactly the same thing!

What makes people look daft to me is when they say a stable 10/20/30/40ohms is better than a stable 200ohms. Your 40ohms is just as useless as 200 of them!!!
 
- Phew..Thanks to all.

OP - now with just a little more insight.

I emerge relatively pleased that I put 2 years inspection in his EIC. I may also invite myself back in the winter to check it again.

As there are some opinions here, would you do more (ie go to install new electrode) - Probably at your own expense? (Yes/No).
1960's house, TT in a village on sandy soil, 2 young children, 30mA RCD and PV on separate 100mA RCD, 198 Ohm Rs, Earth electrode is steel and somewhat rusty, no change in Rs (to nearest 1 ohm) since Autumn 2010.

Rgds

1Justin.
 
- Phew..Thanks to all.

OP - now with just a little more insight.

I emerge relatively pleased that I put 2 years inspection in his EIC. I may also invite myself back in the winter to check it again.

As there are some opinions here, would you do more (ie go to install new electrode) - Probably at your own expense? (Yes/No).
1960's house, TT in a village on sandy soil, 2 young children, 30mA RCD and PV on separate 100mA RCD, 198 Ohm Rs, Earth electrode is steel and somewhat rusty, no change in Rs (to nearest 1 ohm) since Autumn 2010.

Rgds

1Justin.


Would i do the work at my expense ...NO!!

But you tell us, ...What would you do if it were your house, and your two young children??

What do you mean by Rs, ...Zs?? If so, then your stability can be accounted for, by any main bonding connections and possibly your Ra could be a lot higher than the 198 ohms you have stated!!
 
I normally keep out of the great rod debate, but DS makes a very good point which I've yet to see anyone give a direct answer to.... if anywhere between 200 ohms and TN ohms requires additional RCD protection, then it is largely irrelevant what that number is. Its a bit like trying to say that getting caught speeding at 100mph is less illegal than getting caught at 120mph.
 
I normally keep out of the great rod debate, but DS makes a very good point which I've yet to see anyone give a direct answer to.... if anywhere between 200 ohms and TN ohms requires additional RCD protection, then it is largely irrelevant what that number is. Its a bit like trying to say that getting caught speeding at 100mph is less illegal than getting caught at 120mph.

That is the issue in essence....how is accepting Ra's of 10-15 ohms and not accepting 100-200 logical when in the next breath you are scorning reliance on RCD's?

Perfect analogy.
 
- Phew..Thanks to all.

OP - now with just a little more insight.

I emerge relatively pleased that I put 2 years inspection in his EIC. I may also invite myself back in the winter to check it again.

As there are some opinions here, would you do more (ie go to install new electrode) - Probably at your own expense? (Yes/No).
1960's house, TT in a village on sandy soil, 2 young children, 30mA RCD and PV on separate 100mA RCD, 198 Ohm Rs, Earth electrode is steel and somewhat rusty, no change in Rs (to nearest 1 ohm) since Autumn 2010.

Rgds

1Justin.

No. It complies with the regs.If you go down the route of adding more rods how far do you go if it's not coming down to TN values,? if (say) 3 rods gets it to 15 ohms then you are no better off than you were before, so you have to keep going or you've wasted your time.
But I would advise the client of the safety advantages of a 100ma S type upstream of the 30ma on the domestic DB.
 
No. It complies with the regs.If you go down the route of adding more rods how far do you go if it's not coming down to TN values,? if (say) 3 rods gets it to 15 ohms then you are no better off than you were before, so you have to keep going or you've wasted your time.
But I would advise the client of the safety advantages of a 100ma S type upstream of the 30ma on the domestic DB.
then the way forward (after your satisfied the 15 ohms will remain stable) would be to site another rod/s nearby...and link it all up....
 
Trust me mate, if you've whacked in 2 x 1200 x 5/8" rods and you have a reading in the high hundreds as I have done many a time round here then it's gonna take a hell of a lot of work to bring that reading down to a sub ohm value!
 
How so? They both achieve exactly the same thing!

What makes people look daft to me is when they say a stable 10/20/30/40ohms is better than a stable 200ohms. Your 40ohms is just as useless as 200 of them!!!

WTF..did you read my posts FFS, Posts like that make you look a dick.

A resistance of 10Ω is clearly not doing the same as a resistance of 200Ω because the fault current will be higher (Do the ruddy maths and it will prove it)...now as I said in my posts you failed to read I did not say that this was an acceptable reading FFS, so take the earth rod out of your arse, remove the mega and PLEASE read what is said and not what you want it to say so you are all big and winning an argument..when we were not having one in the first place.

If you want my opinion on this, which I have refrained from giving in this thread then it is this...

BSI and the IET committee were wrong to state a 200Ω figure, it should have been 2Ω as a maximum for earth rods. However in my humble opinion any spark who does not achieve a reading, without good reason, of a maximum of 1Ω is failing in their moral responsibility to ensure that all fault currents are cleared effectively and disconnection times will always be compliant no matter what happens to the ground.

Pushing 4 or 5 rods into the ground is not real different from 2 rods, the regulations do not require a single earthing point, only that the earth paths do not overlap for adjacent rods.

I personally have driven five stacks of 4 rods into the ground around a structure to ensure that not only did it have adequate lightning protection but that the Zs reading was around 0.6Ω, and this was stable over many years.

If you investigate and price a job correctly then you should take into account the need to multiple rods, realistically a stack of 3 or 4 rods should meet the needs of the majority of installations to achieve a sub 1Ω Zs, but there is always an exception to the norm.
 
I would like to state the following to those who blindly follow the Regs.

page 2 BS7671:2008 said:
While the publishers and the contributors believe that the information and the guidance given in this work is correct, all parties must rely upon their own skill and judgement when making use of it. Neither the publisher nor any contributor assume any liability to anyone for any loss or damage caused by an error or omission in the work, whether the error or omission is the result of negligence or any other cause. Any and all such liability is disclaimed.

Also:

page 2 BS7671:2008 said:
Users are responsible for its correct application. Compliance with a British Standards cannot confer immunity from legal obligations.

You are responsible for all your work, the Regs are an absolute minimum standard but you are expected, nay, required, to exceed those standards and be professional at all times in how you undertake your works. If you do not agree with the Regs then may I suggest..

page 2 BS7671:2008 said:
It is the constand aim of the IET and the BSI to improve the quality of our products and services. We should be grateful of anyone finding an inaccuracy or ambiguity while using this British Standard would inform the Secretary, G.D.Cronshaw (gcronshaw@----------), The IET, Six Hills Way, STEVENAGE, SG1 2AY, UK
 
That is the issue in essence....how is accepting Ra's of 10-15 ohms and not accepting 100-200 logical when in the next breath you are scorning reliance on RCD's?

Perfect analogy.

It's only a Perfect analogy, to those that can only see fit to twist and/or distort what has been clearly stated on this and other threads.

Still talking around Ra values, because you still can't, or rather don't want to see any other point or aspect except your own. There is absolutely nothing logical about accepting 100/200 ohms as being suitable for the vast majority of TT situations, extremely bad soil conditions would be an exception!! But baseing all TT installations on the lowest possible denominator, such as you seem to think is the way to go, is total nonsense!!

Yep, your right, i do scorn the reliance of RCD devices, and with very good reason!! Perhaps you might too, if you had seen the amount of boxes of RCD devices beeing returned for replacement on the projects i've been involved with, and more noticibly over the last 4 or 5 projects. And were not talking budget devices, but from so-called top of the range manufacturers!! I'm now fully expecting for you, to now come back and say, you have never had, seen or heard of an RCD to fail, ...Right?? lol!!
 
I'm with E54 on the RCD issue, personally I feel the reliance on them is a way to cover up for poor installation design and a lowering of overall standards. Don't get me wrong, used correctly I have no issue with them, but all too often, such as all socket circuits, they are abused and used in a poor way.

The main reason TT systems were required to have an RCD main switch was to abdicate the responsibility of the DNO to provide an adequate earth path that would ensure, at all times, that an installation met the requirements for disconnection times, and if you doubt this, then consider when the RCD requirement was introduced, about 18 months after the newly privatised DNO's commissioned a report that estimated the costs to ensure TT systems met the new requirements would cost them each tens of millions each year for about a decade.

Cynical, damn straight I am, it was corruption pure and simple, it started then and continues now. We need to return to properly designed, installed and verified installations that not only exceed the requirements of BS 7671:2008, but in effect begin the writing of a new standard so things are constantly improving and not being watered down for commercial interests of the big players and the DNO's.
 