OK. On a more practical note, might I stand a chance of getting 5/8" (16mm) rod with a standard Makita 780W 2.9Kg hammer? - Or would I need to rent a big boy ?
No. It complies with the regs.If you go down the route of adding more rods how far do you go if it's not coming down to TN values,? if (say) 3 rods gets it to 15 ohms then you are no better off than you were before, so you have to keep going or you've wasted your time.
But I would advise the client of the safety advantages of a 100ma S type upstream of the 30ma on the domestic DB.
WTF..did you read my posts FFS, Posts like that make you look a dick.
A resistance of 10Ω is clearly not doing the same as a resistance of 200Ω because the fault current will be higher (Do the ruddy maths and it will prove it)...now as I said in my posts you failed to read I did not say that this was an acceptable reading FFS, so take the earth rod out of your arse, remove the mega and PLEASE read what is said and not what you want it to say so you are all big and winning an argument..when we were not having one in the first place.
If you want my opinion on this, which I have refrained from giving in this thread then it is this...
BSI and the IET committee were wrong to state a 200Ω figure, it should have been 2Ω as a maximum for earth rods. However in my humble opinion any spark who does not achieve a reading, without good reason, of a maximum of 1Ω is failing in their moral responsibility to ensure that all fault currents are cleared effectively and disconnection times will always be compliant no matter what happens to the ground.
Pushing 4 or 5 rods into the ground is not real different from 2 rods, the regulations do not require a single earthing point, only that the earth paths do not overlap for adjacent rods.
I personally have driven five stacks of 4 rods into the ground around a structure to ensure that not only did it have adequate lightning protection but that the Zs reading was around 0.6Ω, and this was stable over many years.
If you investigate and price a job correctly then you should take into account the need to multiple rods, realistically a stack of 3 or 4 rods should meet the needs of the majority of installations to achieve a sub 1Ω Zs, but there is always an exception to the norm.
I'm afraid they only see what they want to see, and then twist and/or distort to suite they're position. The rest will be totally ignored, because it isn't in BS7671/OSG, that they steadfastly have to stand behind, as a way or an excuse of not having to do anything!!
OK. On a more practical note, might I stand a chance of getting 5/8" (16mm) rod with a standard Makita 780W 2.9Kg hammer? - Or would I need to rent a big boy ?
Trust me mate, if you've whacked in 2 x 1200 x 5/8" rods and you have a reading in the high hundreds as I have done many a time round here then it's gonna take a hell of a lot of work to bring that reading down to a sub ohm value!
How so? They both achieve exactly the same thing!
What makes people look daft to me is when they say a stable 10/20/30/40ohms is better than a stable 200ohms. Your 40ohms is just as useless as 200 of them!!!
I've avoided this thread because I think the UK regs on acceptable TT rod impedances are unsatisfactory and putting all your eggs in one basket with RCD protection is not good practice but clearly the UK regs make provision for it so who would I be to preach any differently?
That said, given that as a UK electrician you're entitled to work to the value given so I can understand why you feel the 10/20/30/40ohms or 200 ohms makes no difference but I still disagree. I'd be more inclined to agree if the system earth's only function was to protect against overload currents and guarantee disconnection times .....but it isn't. The earth is functional also and especially nowadays with SMPS's, variable frequency motor controllers and surge arrestors it carries a considerable amount of standing leakage with a good possibility of a considerable amount more if certain power conditions occur. High earth impedances can adversely affect the functionality of devices and it can also encourage galvanic corrosion of pipework, hot water cylinders etc.
I'm happy to agree to disagree but I'm firmly in the camp of a low Ra being far better than a high one on any earthing arrangement including TT regardless of what's in the regs.
I would agree completely where there are likely to be high earth leakage currents. However on the kind of small TT installs commonly queried on this forum that is not likely to be an issue.
WTF..did you read my posts FFS, Posts like that make you look a dick.
so take the earth rod out of your arse, remove the mega and PLEASE read what is said and not what you want it to say so you are all big and winning an argument..when we were not having one in the first place.
And this is where your side of the argument ceases to hold any credability at all. That's me done I think.
Not so, on say a medium sized commercial/industrial premises.