How to test an earth electrode resistance for Lightning Protection System in the middle of large concrete pad? I cannot not find a soft ground for spikes to drive in for testing. Is there any other ways of measuring the earth electrode resistance value?
Laxi
Have a look at hiring (or purchase at £500+) an earth resistance clamp which induces a current into the system without you needing to disconnect the main earth.
Or, as above an impedance test
The trouble with those earth clamps, is that you need room to get the jaws around the earth rod, and there is generally very little room to do this when earth rods are within a flush to ground earth pit...
EDIT... How many electrodes (earth rods) are there along each side of the building being tested and how far apart are they?
Hi,
Thanks for your help on this matter. I am actually testing earth rod resistance for Lightning Protection System. There are four down conductors on each corner of the building. I managed to measure all three earth rod resistance value. But there is no soft ground around the electrode rod that belongs to fourth down conductor. One 2 m long copper solid rod is being used on this down conductor . The nearest soft ground is approximately 40m away from the test point. The surrounding area is concrete pad.
Is there any means of testing the earth electrode resistance for Lightning Protection System?
Laxi
Unless this building is very small say 10m to 15m square, then it doesn't sound like you have enough down conductors depending on what the building is and building construction material.
You could use weighted metal plates in contact with ''wet'' concrete in place of your test spikes and compare values with that of the other 3 earth rods. BTW i've more often than not used test leads in excess of a 100m for the C1 test spike. So 40m isn't, as far as i'm concerned any great distance when testing earth rods...
Hi,
Laxi
if you are using Megger equipment to do your testing there is no need to sink the spikes if you can't. Speak to Megger technical and they will walk you through the test procedure.
Reply to Earth Electrode Testing in the UK Electrical Forum area at ElectriciansForums.net
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...