There was an MTI brekkie morning at our CEF a while back and I looked at an ETHOS earth leakage clamp which was around a hundred quid. It would only measure leakage current by clamping both tails,(that was stated in the manual), the guy told me all the cheaper clamps work like that and will not read milliamps from a single conductor. If that is incorrect it was from the horses mouth so to speak.

That's two seperate things, the ability to measure milliamps and measuring leakage aren't the same thing.

The ability to measure milliamps simply means that the meter is capable of measuring small currents.

The only way I know of measuring leakage current is by clamping all live conductors of the circuit in question. Clamping the cpc won't tell you the leakage due to the parallel paths involved, plus the leakage may not be to the cpc of the circuit.
 