It’s a bad setup but I went for a call out in the night in a residential unit.
There’s a rcd in its own enclosure feeding a 14 way board that had tripped.
I reset it didn’t trip.
I passed 2 mornings later and still hadn’t tripped.
Whilst there on first visit I stuck my earth leakage clamp around the outgoing rcd tails and
Around 9amps
Fluctuating next minute was 6amps

also similar amps around main earth.
The biggest culprit and most likely was outside lights which dropped it from 9amps to 2.5
Another lighting circuit dropped it to 1 amp when both off.

how was there 9amps imbalance on tails and 30ma rcd not tripping ?
I forgot to do a ramp test.
 
Hi - not sure I understand correctly, but if there was 9A in the means of earthing conductor, that would indicate a direct N-E fault AND the RCD would likely be faulty too ...
 
Hi
It’s a bad setup but I went for a call out in the night in a residential unit.
There’s a rcd in its own enclosure feeding a 14 way board that had tripped.
I reset it didn’t trip.
I passed 2 mornings later and still hadn’t tripped.
Whilst there on first visit I stuck my earth leakage clamp around the outgoing rcd tails and
Around 9amps
Fluctuating next minute was 6amps

also similar amps around main earth.
The biggest culprit and most likely was outside lights which dropped it from 9amps to 2.5
Another lighting circuit dropped it to 1 amp when both off.

how was there 9amps imbalance on tails and 30ma rcd not tripping ?
I forgot to do a ramp test.
Do you mean milliamps
 
are you sure of the following?

meter was positioned correctly round all the relevant cores
you are reading the correct scale on the meter

9mA would be acceptable
9A is huge, it suggests that there is over 2kw of energy being dissipated by a live to earth fault.

if that is the case then you have both a faulty rcd and a fault that i am surprised has not already started a FIRE
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Wilson12

Trainee
-
Joined
Location
London
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Earth leakage clamp meter
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Wilson12,
Last reply from
James,
Replies
3
Views
1,676

Advert

Back
Top