Hi
It’s a bad setup but I went for a call out in the night in a residential unit.
There’s a rcd in its own enclosure feeding a 14 way board that had tripped.
I reset it didn’t trip.
I passed 2 mornings later and still hadn’t tripped.
Whilst there on first visit I stuck my earth leakage clamp around the outgoing rcd tails and
Around 9amps
Fluctuating next minute was 6amps

also similar amps around main earth.
The biggest culprit and most likely was outside lights which dropped it from 9amps to 2.5
Another lighting circuit dropped it to 1 amp when both off.

how was there 9amps imbalance on tails and 30ma rcd not tripping ?
I forgot to do a ramp test.
 
Hi - not sure I understand correctly, but if there was 9A in the means of earthing conductor, that would indicate a direct N-E fault AND the RCD would likely be faulty too ...
 
Hi
It’s a bad setup but I went for a call out in the night in a residential unit.
There’s a rcd in its own enclosure feeding a 14 way board that had tripped.
I reset it didn’t trip.
I passed 2 mornings later and still hadn’t tripped.
Whilst there on first visit I stuck my earth leakage clamp around the outgoing rcd tails and
Around 9amps
Fluctuating next minute was 6amps

also similar amps around main earth.
The biggest culprit and most likely was outside lights which dropped it from 9amps to 2.5
Another lighting circuit dropped it to 1 amp when both off.

how was there 9amps imbalance on tails and 30ma rcd not tripping ?
I forgot to do a ramp test.
Do you mean milliamps
 
are you sure of the following?

meter was positioned correctly round all the relevant cores
you are reading the correct scale on the meter

9mA would be acceptable
9A is huge, it suggests that there is over 2kw of energy being dissipated by a live to earth fault.

if that is the case then you have both a faulty rcd and a fault that i am surprised has not already started a FIRE
 

Reply to Earth leakage clamp meter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
1
Views
951
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
7
Views
2K
I WAS ONCE SHOWN HOW TO CALCULATE INSULATION RESISTANCE USING A CLAMP METER. SO I NEED HELP AS IVE FORGOTTEN. CAN ANYONE HELP WITH THIS FOLLOWING...
Replies
4
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock