Discuss MEASUREMENT OF LEAKAGE CURRENT in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Farmelectrics
I WAS ONCE SHOWN HOW TO CALCULATE INSULATION RESISTANCE USING A CLAMP METER. SO I NEED HELP AS IVE FORGOTTEN. CAN ANYONE HELP WITH THIS FOLLOWING FORMULA 230 + (20X10-6) = 11.5Mohms how have the arrived at this. A clamp meter has been clamped around live and neutral tails at the consumer and 2mili amps leakage 0.02mA is apparently 20micro joules. HELP
  • INSULATION RESISTANCE WITH A CLAMP METER.pdf
You've copied the (admittedly fuzzy) formula from the document wrongly. It's division, not '+'
Resistance = voltage divided by current!
and of course 20 times 10 to the power of -6 for micro amps 🙂
0.02mA is 20 microamps! Not 2 milliamps
And keep away from Joules - you want ohms law and resistance, not energy!
PS you would normally want to measure insulation resistance at increased voltage, eg 500v or 1kV if in doubt about condition of the wiring, so the clamp meter method is not ideal!
sum is 230/(20x10^-6) ohms
Same as 230/20 x 10^6
= 11.5 x 10^6 ohms
= 11.5 Megohms (or Megaohms if you prefer!)
= 11.5 x 10^6 ohms
THANKS FOR YOUR HELP AVO
Reply to MEASUREMENT OF LEAKAGE CURRENT in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Hi ! Much talk of the use of type A, type B and Type F RCDs recently. As we know all are specified at varying levels to ignore the blinding...
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
4K