Have any of your 4 gang adaptors got surge protection in them? I have had a few which can show 0.1 meg ohms down to earth. They could cause the rcd to trip?
Yeah checked my daughters (new) hairdryer. 5ma at the plug, 5ma extra at the cu. So does seem to tally. If a single device can create 5ma leakage or even 8ma for the kettle then surely my readings of 15ma leakage current at base level is fairly normal? Turning my computers on seem to cause a spike of around 10 to 15ma so causes trip. Does this all sound normal then? Is it just to be expected? Can't be every device in my house is faulty so these amounts must be normal?
I like the sound of earth neutral fault, something concrete to investigate. I guess I need an electrician to do better tests.
Wait and get the electrician to insulation test the kettle.Thanks for all the help, even though I haven't got to the bottom of this. I feel like I understand what's going on a bit more. I think what I'm going to do is get an electrician to fit rcbos to each circuit and then have all the wiring tested.
I have a feeling that there's not a lot actually wrong, I'm just running too many devices that leak to earth. That kettle for example I've tested a number of times and does seem to leak 10ma, so that's going in the bin.
If there is an earth neutral fault I think I need an electrician I can't find it myself.
I will report back I promise. It's been very interesting investigating it all. One small update, I found 2 x surge protector 4 gang extensions and 1 ikea USB 4 gang hidden away in bedrooms. So they might have been creating some leakage. They are all binned now. I get extremely weird readings from my earth wire from CU. The line and neutral clamped gives relatively sensible readings - I've noticed that the placement of the wires in the clamp need to be exactly central and not twisted otherwise you get wild readings. The earth wire from CU shows higher leakage than the live-neutral, and it seems to react to load much more than the live-neutral. Also I measure 90ma on my gas pipe yesterday. All very interesting (and annoying).Wait and get the electrician to insulation test the kettle.
Whichever way, come back and tell us the outcome.
As @Avo Mk8Ive been testing and have found lots of strange behaviour that I don't understand.
1. The lighting circuit and main socket ring seem to be connected somehow. When lighting circuit is on about 3v can be detected neutral/earth on socket ring. Goes to zero if I trip lighting breaker Same the other way round, with ring on and lights off there's a voltage on lighting neutral/earth. This is while all neutrals are disconnected from cu. Earths still connected. So I think there is a connection between live and earth and voltage is flowing back from earth to all the neutrals.
2. With power off and every device unplugged. I have a measurable resistance between neutral and earth everywhere on my ring. Slightly lower resistance on the middle floor. Ive opened every socket and can't find a smoking gun. I have separated the ring and both sides still have earth to neutral connection with slightly different resistance. If I turn lighting circuit on/off it affects the resistance on the socket ring. When I have more time i will spend longer disconnecting more parts of the ring and see if i can find where it's coming from.