Yeah checked my daughters (new) hairdryer. 5ma at the plug, 5ma extra at the cu. So does seem to tally. If a single device can create 5ma leakage or even 8ma for the kettle then surely my readings of 15ma leakage current at base level is fairly normal? Turning my computers on seem to cause a spike of around 10 to 15ma so causes trip. Does this all sound normal then? Is it just to be expected? Can't be every device in my house is faulty so these amounts must be normal?

I like the sound of earth neutral fault, something concrete to investigate. I guess I need an electrician to do better tests.

A class 2 appliance shouldn’t cause a rise in earth leakage not unless there’s a problem with neutral current being diverted.

The problem may not even be in your property, without proper testing it’s all guess work.

What adds up is that your kettle causes more leakage than the hair dryer so seems to tally with the theory more load more leakage
 
The first thing to do is to invite Mr. Bainbridge back to carry out another EICR. Interesting that he recommended a retest after 5 years instead of the normal 10 for domestic. This might indicate there were some concerns about the wiring and that it might be failing.
I assume that the EV point has been installed since 2014, since the incorrect make of the RCD and its poor fitting should render a report 'unsatisfactory.'
 
Thanks for all the help, even though I haven't got to the bottom of this. I feel like I understand what's going on a bit more. I think what I'm going to do is get an electrician to fit rcbos to each circuit and then have all the wiring tested.

I have a feeling that there's not a lot actually wrong, I'm just running too many devices that leak to earth. That kettle for example I've tested a number of times and does seem to leak 10ma, so that's going in the bin.

If there is an earth neutral fault I think I need an electrician I can't find it myself.
 
Thanks for all the help, even though I haven't got to the bottom of this. I feel like I understand what's going on a bit more. I think what I'm going to do is get an electrician to fit rcbos to each circuit and then have all the wiring tested.

I have a feeling that there's not a lot actually wrong, I'm just running too many devices that leak to earth. That kettle for example I've tested a number of times and does seem to leak 10ma, so that's going in the bin.

If there is an earth neutral fault I think I need an electrician I can't find it myself.
Wait and get the electrician to insulation test the kettle.

Whichever way, come back and tell us the outcome.
 
Wait and get the electrician to insulation test the kettle.

Whichever way, come back and tell us the outcome.
I will report back I promise. It's been very interesting investigating it all. One small update, I found 2 x surge protector 4 gang extensions and 1 ikea USB 4 gang hidden away in bedrooms. So they might have been creating some leakage. They are all binned now. I get extremely weird readings from my earth wire from CU. The line and neutral clamped gives relatively sensible readings - I've noticed that the placement of the wires in the clamp need to be exactly central and not twisted otherwise you get wild readings. The earth wire from CU shows higher leakage than the live-neutral, and it seems to react to load much more than the live-neutral. Also I measure 90ma on my gas pipe yesterday. All very interesting (and annoying).
 
If it's a tnc-s pme supply you would expect to protective bonding conductors to carry some current.
Have you tested your meter on a fixed small load?
 
Could a slightly resistive joint in the neutral supply to the property be the cause of this? The higher the load in the property, the more the neutral and earth terminal at the consumer terminals will move above true earth, giving rise to the current in the gas bond.
 
Small update... I couldn't help doing a bit more investigation so I had a look at the wiring in cu. I think I'm allowed to do this?
Some observations below:
1.I noticed a dead short between earth and neutral on the neutral bar associated with non kitchen rcd. However the next day when I checked it had risen back to 2ohms. Other neutral bar and main neutral in around 2ohms to earth bar today. Yesterday showed higher, around 10ohms for both.
2.i checked various plugs on house ring and all had dead short between neutral and earth. However if I hold the multimeter there it keeps jumping up to 2ohms and then back to short.
3. Kitchen ring showed higher value, 3- 5ohms and was pretty stable.
4. I disconnected cu neutrals of non Kitchen ring and checked continuity, both ends of ring connected, resistance around 2-3ohms.
5. Checked disconnected neutral to earth, multimeter struggled to stabilise. Fluctuated, but around the 10mohm range. Always showed a figure, never an OL.
6. My disconnected lighting circuit neutral to earth was OL - no connection.

Does this sound like a fault somewhere on the ring where earth and neutral are touching but only just? Next steps to look at the sockets for any knicked wires?
 
If you can measure any resistance between earth and neutral on an ordinary multimeter with the main switch and RCDs off, then you have a fault. The 'correct' tool for this test applies a much higher voltage (up to 1000V) and will measure higher resistances than a multimeter.
We can only advise against you opening up the CU, but since you have anyway, disconnect both neutrals and cpcs for the ring final in question, then pick a socket which is logically near the middle of the RFC, disconnect that, and test the resulting two halves of the circuit. Repeat the process on the faulty half and again, until you find the fault.
 
Ive been testing and have found lots of strange behaviour that I don't understand.

1. The lighting circuit and main socket ring seem to be connected somehow. When lighting circuit is on about 3v can be detected neutral/earth on socket ring. Goes to zero if I trip lighting breaker Same the other way round, with ring on and lights off there's a voltage on lighting neutral/earth. This is while all neutrals are disconnected from cu. Earths still connected. So I think there is a connection between live and earth and voltage is flowing back from earth to all the neutrals.
2. With power off and every device unplugged. I have a measurable resistance between neutral and earth everywhere on my ring. Slightly lower resistance on the middle floor. Ive opened every socket and can't find a smoking gun. I have separated the ring and both sides still have earth to neutral connection with slightly different resistance. If I turn lighting circuit on/off it affects the resistance on the socket ring. When I have more time i will spend longer disconnecting more parts of the ring and see if i can find where it's coming from.
 
Ideally testing really requires an understanding of the circuit under test, and a plan of what to measure where. I'm finding it a little difficult to unravel your findings, so grateful if you could clarify:

1. Are you saying that with both ring neutrals disconnected from the neutral bar in the CU, there is a voltage between those neutrals to earth when the lighting circuit is on, but not when lighting is off?
Assuming you are using a typical high impedance multimeter, that could be explained by capacitative coupling between the two circuits, if the lighting and ring cables run parallel or close to each other somewhere in the house. Often referred to as a 'ghost voltage'. It typically disappears when any load is placed on it. It is not necessarily indicative of a fault.

2. Is your initial statement about measurable resistance made with the relevant RCCB on or off? It would also be helpful if you gave values for the "measurable resistance" you've found, bearing in mind neutral and earth are connected together at supply 'source' (somewhere). Nevertheless there's often a small voltage between the two, depending on demand outside your property, which might affect multimeter resistance readings when the RCCB is on.

If (with everything off) you've taken both ring neutrals out of their bar in the CU, and you still have a very low resistance reading between them and earth, you surely have a fault or cross-connection somewhere on that ring, or something like a defunct immersion heater!

If your testing shows up specific low resistance readings between N and E with the circuit under test completely disconnected, and the cause is not obvious, get an electrician in!
 
Ive been testing and have found lots of strange behaviour that I don't understand.

1. The lighting circuit and main socket ring seem to be connected somehow. When lighting circuit is on about 3v can be detected neutral/earth on socket ring. Goes to zero if I trip lighting breaker Same the other way round, with ring on and lights off there's a voltage on lighting neutral/earth. This is while all neutrals are disconnected from cu. Earths still connected. So I think there is a connection between live and earth and voltage is flowing back from earth to all the neutrals.
2. With power off and every device unplugged. I have a measurable resistance between neutral and earth everywhere on my ring. Slightly lower resistance on the middle floor. Ive opened every socket and can't find a smoking gun. I have separated the ring and both sides still have earth to neutral connection with slightly different resistance. If I turn lighting circuit on/off it affects the resistance on the socket ring. When I have more time i will spend longer disconnecting more parts of the ring and see if i can find where it's coming from.
As @Avo Mk8

You need some proper test gear and someone who can use it.

Otherwise circles come to mind.
 
Firstly thanks for sticking with me, clearly I'm getting to the point where I need an electrician. I think they will suggest a house rewire and I can't really afford it hence trying myself. But ultimately yes I totally get it in the end I will have to get someone really good in to look at this.


To answer previous questions just in case...

1. The ring neutrals are disconnected from the cu but the lighting neutral is also disconnected. Neither circuit had any current flowing without neutrals. But still voltage found its way across to the neutral of the ring, i presume via earth? But i didnt know about ghost voltage and it's only small so perhaps like you say it's within normal range. I do know about capacitive coupling, I thought that was when there was a missing earth?
2. With the ring neutrals and earth disconnected from cu I register in the range of 10 to 20 Mohms between earth and neutrals wires of the ring. I know the earth and neutral are connected at my supply so I have disconnected all the ring wires from cu to test them in isolation. All devices are unplugged but I do have some USB sockets that may be messing with this reading I suppose.

My multimeter isnt a really cheap one, I do work with electronics in my proper job so I do have some experience with the basics. But I don't believe it has a high voltage for resistance testing so it may be insufficient for this.
 
Last edited:
Any neutral disconnected will become live though a load,maybe even if the load is off.
Capacitive coupling can happen between any conductors close to any other.
We test IR at 500 volts so getting a high reading at a few volts does not mean a lot.
 