Discuss Earth Rod Path to CU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi All,
I am installing a new earth rod in my house renovation and was wondering what the regulations state in regards to routing the 16mm cable back to the CU.
Does the cable have to route under the ground or can it enter the building above ground?
If above, is there any specific methods of doing this?
I saw a YouTube video that used an isolated strips attached to the outside wall (
), now i can't seem to see this method mentioned anywhere else or where to buy these from?
Any assistance would be great.
Cheers.
Jamie
That video is of a French installation, so you won't find the products used there in this country.
The obvious response to this is to advise asking the electrician who will be doing the work and testing it to advise.
The top of the earth rod should be enclosed in a suitable access box for inspection and testing, the earthing conductor can be buried and enter the building above or below ground but suitable protection may be needed for the portion below ground level.
Are you sure that one earth rod will be enough to give a reliable, stable and suitably low resistance connection to earth? Generally more than one rod is required to get a good Ra value.
Thanks for your reply.
I have considered using an additional rod yes and most probably will include 1 more.
With it being French, that makes more sense!
I will speak to the electrician signing the work off for me, but I think you have answered what i am after.
The cable will be enclosed in a form of protective housing, does this have to be metallic or can it be PVC? Im guessing this is more for corrosion protection than it being broken?
The minimum size for an Earthing conductor buried in the ground is 2.5mm2 if provided with mechanical protection and protection against corrosion (sheath or insulation).
For an Earthing conductor that is sheathed but not mechanically protected, the minimum size is 16mm2.
Table 54.1 is your guide.
I’m afraid that your approach to a TT earthing system is a little more complicated than your proposal. Let your electrician do it for you as the Ra will need measuring etc
How long are you intending to make each rod? What space do you have available for the installation of these rods, they need to be correctly spaced to get the best results.
I am intending on using plastic conduit to protect within the ground.
I have also purchased another rod and a T joint to join both together, as they will be in parallel then the resistance should be greatly reduced. I am quite sure 1 will be good enough for the soil in the area, I will get my electrician friend to measure the Ra before installing a secondary pole.
the path can be anything you want.... concrete, tarmac, block paving, crazy paving, slabs, the list is endless. :D:D:D.
Do you have a link to the T joint, or even a picture? It's not something I've come across before and am. Interested to know.
What makes you say you are sure one rod will be enough? How long is this rod going to be?
Reply to Earth Rod Path to CU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi all, looking for a bit of advice and confirmation on my proposed plans for a SWA sub main to a ISO metal storage container. I've calculated the...