Discuss Earthing arrangement advice please in the UK Electrical Forum area at ElectriciansForums.net
Dave 85
Hi lads
Looked at a job today
3036 Fuseboard
Looks like TT but only 2.5mm earths visible, couldn't find a stake and 126ohms Ze on a wet day.
There is an old earth leakage breaker, it did not trip when put under 500mA RCD test, does this mean its f***ked?
The supply fuse looks Like a TNCS head but no earth coming out of it. I take it I cant just PME it of my own accord?
This would be ideal as the outside seems to be concrete everywhere so getting a stake in would be a challenge.
Im gonna recommend a new CU to the client. If they dont go for this is it acceptable to replace the earth trip with a 100mA RCD?
Im also recommending upgade of main earth and bonding but need to know for def that PME'ing is out of the question.....
Any advice would be very much appreciated
Oh yeah...here are some photos...
That unit is a VO-ELCB, putting any amount of mA through it won't make it do anything due to it being VO (voltage operated).
These units are obsolete now as many of them have malfunctioned and should be removed/upgraded sooner rather than later.
I wouldn't attempt to test that Voltage trip, I pushed the test button on one once just messsing around when I was apprentice and we ended up replacing it with an RCD for free, the customer said 'it was fine before you touched it'!
If a VOELCB on a TT system fails to operate when tested with an instrument or integral test button, this would warrant a Classification Code C2 (potentially dangerous).
But, subject to the VOELCB being proved to operate correctly, continued reliance on it for fault protection (protection against indirect contact) would normally warrant a Classification Code C3 (improvement recommended).
However, if the VOELCB relies on a water pipe not permitted by Regulation 542.2.4 to be a means of earthing, this should attract a Classification Code C2 (potentially dangerous).
From ESC
Reply to Earthing arrangement advice please in the UK Electrical Forum area at ElectriciansForums.net
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...