Discuss Earthing & Bonding - Steel framed Building in the UK Electrical Forum area at ElectriciansForums.net
J
John1981
Hi.
We're currently carrying out an installation in a large steel framed building on an agricultural property.
Supply in, is TNS. Supply intake is approx 225m from the new building. We require an 80a 3 phase supply, which has been sized at a 95mm SWA with a 25mm CPC. 300ma TD RCD on main board in new build. Due to it's steel frame nature we're intending to bond the S/Steel work, but we've now just found out there's going to be steel Biomass pipes entering the building from underground. I know on a TNS supply, maximum equipotential bonding CSA is 25mm. Anyone any idea on how to treat this whole earthing situation before i drive into the regs. Are we to bond the extraneous conductive parts with a separate bonding conductor back to the MET? Technically the building itself is an earth electrode. My concern is of that the earthing and bonding conductors via the SWA and 25mm will be undersized? Any opinions would be greatly appreciated.
work out your Zs at the steel framed building by adding the Ze to the calculated R1+R2 of the 95mm+25mm, then work out yout PEFC. from that, use the adiabatic equation to determine the min csa for cpc.
Reply to Earthing & Bonding - Steel framed Building in the UK Electrical Forum area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth...
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...