It is in GN8 mate, this tells us each flat is to be considered as a seperate installation, this also goes for HMO's (houses of multiple occupancy), bedsits and the like, and it refers you to reg 411.1.3.2 for the electrical definitions, I have posted the relevant info. on the forum before (pages from GN8).
There have been some rather longwinded posts on here before also regarding this subject.
It is so each flat has it's own equipotential zone, and as BS7671 requires each installation to have main bonding conductors, GN8 elaborates on this, and specifically says this applies to multi occupancy buildings and classes each flat as a seperate installation and also elaborates on the definitions given in the reg number above.
Edit:, I was not having a dig at anyone, just posting the information which some people may find informative and useful, as not everyone has GN8, even GN8 itself states that the regs regarding this are not clear, and are often misunderstood/misinterpreted.