The situation at hand is as follows:
Due to the potential of voltage between the PME earth and true earth, and as stated in 717.411.4, it cannot just be connected to the PME (even if caravan owners do this themselves all the time, but that's their choice, their risk, and no one else's liability).
Ideas I've come up with:
If I could put in an earth rod and separate it from the house, and avoid simultaneous contact with the outside light by adding a fused spur unit next to the commando socket to power the outside light, and putting in a kinetic switch (and pulling out the cable currently supplying the light). But that still leaves simultaneous contact potential with the neighbour's caravan (pretty sure that's on PME when connected).
Connecting an earth rod to the PME isn't realistically likely to provide a low enough reading by itself to keep under 50V if load is being drawn during a PEN fault.
I thought about trying to find a PEN fault device normally used for car chargers, but I'd be outside the manufacturers intended use, hoping it works for something drawing a lower load than a car charger would, so if it didn't work then that's entirely on me.
Leaning towards my first idea, as the chances of simultaneous contact, and both caravans being plugged in, and there being unsafe voltage between them all at once seems pretty unlikely. But do anyone else have any insight or ideas?
- house with a PME supply
- caravan sitting directly on the ground (on the lawn)
- simultaneous contact potential with outside light by the front door (decorative and not class 2) on one side, and with the neighbour's caravan on the other
- no sign of a dedicated charging point or earth rod that I can see on the neighbours side, so I would assume they're just plugging it in through the window to charge occasionally, and I can practically guarantee they're also on PME
- customers intention is that a family member will be basically living in the caravan