Correct. In all the "what if ..." scenarios, you can't control what someone comes along and plugs in. If their new genny is either centre-tapped to earth, or more likely, is 55-0-165V, then linking N-E anywhere is going to cause a problem - and I suspect few of them have 2 pole overloads meaning that you'd have a shorted winding with no overcurrent protection.I was thinking about this again today and one downside I thought of was the chances of someone plugging a centre tapped earth generator into a system with a linked neutral and earth. This would short it out and potentially cause damage.
If you made a "special" lead with the N-E link, then either it doesn't get used (a different lead without it leads to an IT supply), or that lead gets used elsewhere and causes problems.
That's probably a fair assessment. I think the only thing that can be said for certain is that it's impossible to do in a generic way - i.e. where you aren't in a controlled environment where things can't get swapped about without someone with sufficient skill overseeing it for safety.You can’t win either way and tbh my feeling is most generator installs I’ve seen don’t seem all that safe and the installer has probably just ‘winged it’.
You either create a risk of shorting out a genny (put N-E link in the fixed installation, replacement genny isn't floating), or you risk having an IT supply (put N-E link in genny, replacement genny doesn't have it). About the only way I can think of doing it is to fit a N-E resistor in the fixed installation downstream of the RCD - if the genny isn't floating then the RCD will trip, if the genny is floating then the resistor will create enough fault current to cause downstream RCDs to trip (like using an RCD where there isn't a good enough earth electrode on a TT supply). But that won't be standards compliant either, and there's a risk of nuisance tripping if the genny does have a N-E link.
Note to self ... must check how my genny is wired.


) to connect them. These cottages were in a large piece of land they owned, and after hearing about the generator they'd tried, I suggested they consider a submain from another property (1300 m away) - stressing they'd need to get someone who knew what they were doing to size it.