Thankyou for your detailed response.Looking at the diagrams it has a schematic at the end:
Looks like a 3-phase alternator and the "control unit" might be the inverter that converts rectified DC off that to good sine-like single phase AC. However, there are no RCD on the outputs and I'm guessing the floating supply approach is the means of reducing the risk of shock on contact with a live conductor instead of ADS from a RCD.
Without modifying the generator (not a trivial task) you can't really win:
Also the instructions are clearly for the USA market, in spite of it being sold here with UK outlets:
- Earth the neutral some place and you have no additional protection on the generator's socket outlets, against the regs. Also if you ever use a properly engineered generaotr with RCD it will trip as a result of the link.
- Don't earth the neutral and the house has an IT supply without skilled supervision, also against regs
Use a ground fault circuit interrupter (GFCI) in damp areas and areas containing conductive material such as metal decking.
Connection to your home’s electrical system requires a listed 30A transfer switch installed by a licensed electrician and approved by the local authority having jurisdiction. The connection must isolate the generator from the utility power and must comply with all applicable laws and electrical codes.
Do not use generator for medical and life support uses.
In case of emergency, call 911 immediately.
That also fits, as the USA typically has N-E links in the incoming panel/DB, so the issue of a floating supply is not happening. I don't know if they have any similar blanket RCD rules on socket outlets as we do.
Shows the level of quality when the warranty is limited to 1000Hrs for domestic use and 500Hrs for industrial and commercial useChampion 3600 Watt Frame Type Inverter
Champion 3600 Watt Digital Hybrid Petrol Generator. Portable and easy to move. Wireless key start. Perfect for backup power, home use and even camping in the UK.www.championpowerequipment.co.uk
Probably the least-worst option.I would go with option A
consider the inlet on the house as the origin of supply and link N to E at that point.
5kva continuous so I have a 20A double pole mcb on the output side. I am looking for a cheap 10KVA on ebay so that I can use the full output of the generator.To make the 55-0-55 part of the system true reduced-low-voltage, the centre-tap of the generator output should be referenced to earth. There should be no connection to the centre-tap of the transformer otherwise circulating currents will occur unless the voltage symmetry is perfect. However, the interwinding screen, if there is one, should be earthed. This would mean separating any internal connection that might exist between the screen and the CT. The screen would otherwise be at an 'artificial' neutral held halfway between the two live conductors by the transformer itself. Not a big deal but not technically correct. I can't see any advantage to making this part of the system 110V TN.
The two sides of the transformer are electrically separate so it shouldn't matter whether the earthing systems are interconnected or not. The output of the transformer, with N-E linked, is regular TN-S so that just needs an earth reference as well.
Are you providing thermal protection to the transformer, and if so, how? Is the 5kVA rating intermittent or continuous? (just trying to visualise the tranny). How close has the output voltage worked out in practice? I'm expecting some contributors here to be thinking that this is a cheeky way to get 230V but TBH it's the sort of thing I would do so I'm not shooting it down!
Thanks. what happened was I got a 7KVA road tow lighting tower really cheaply (£385) because it was advertised as 110V only. It has a 1500RPM Kubota diesel engine and runs great. I want to keep using the lights from time to time, and it also has a couple of 110V CTE outlets. I thought I could be clever and change the jumpers on the generator, but it is 55-0-55 only.To make the 55-0-55 part of the system true reduced-low-voltage, the centre-tap of the generator output should be referenced to earth. There should be no connection to the centre-tap of the transformer otherwise circulating currents will occur unless the voltage symmetry is perfect. However, the interwinding screen, if there is one, should be earthed. This would mean separating any internal connection that might exist between the screen and the CT. The screen would otherwise be at an 'artificial' neutral held halfway between the two live conductors by the transformer itself. Not a big deal but not technically correct. I can't see any advantage to making this part of the system 110V TN.
The two sides of the transformer are electrically separate so it shouldn't matter whether the earthing systems are interconnected or not. The output of the transformer, with N-E linked, is regular TN-S so that just needs an earth reference as well.
Are you providing thermal protection to the transformer, and if so, how? Is the 5kVA rating intermittent or continuous? (just trying to visualise the tranny). How close has the output voltage worked out in practice? I'm expecting some contributors here to be thinking that this is a cheeky way to get 230V but TBH it's the sort of thing I would do so I'm not shooting it down!