Discuss EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net
No it’s not correct.
There is no requirement to install RCDs in Consumer Units.
There are requirements to protect some circuits, which would require an RCD be placed in or very close to the Consumer Unit.
However, the person who conducted the Inspection should be listing the instances where RCD protection is required but not been provided, and then applying a code for each of those instances.
In many instances, RCD protection can be provided, simply by the installation of an RCD or RCBO in or close to the Consumer Unit.
Only thing that’s changed, is the person who conducted the latest inspection, wants to make money from you.
Hi been using the Napit Code breaker for a few year now and if I see none or a lack of RCD protection for circuits not clipped direct or in trunking or conduit its a straight C2
just on the grounds of section 5.12.3, 522.6.202, no protection of cables in wall less than 50mm from surface, which can not always see but can assume if the wall is a standard 100mm wall, that it does not conform, we sparkies are not looking to rip people off as Ive seen peeps on here giving good sparks a bad name on for telling folks you got to spend money on your property to get it to a good and safe standard etc. as introducing RCD's or RCBO's also detects any Earth to Neutral defects if not already identified on the EICR
this is just my opinion and my clients will have a chose to do it or not.
Regards Jelade Electrical Services
This is at odds with Best Practice Guide 4, which codes it as C3
Hi Everyone.
I have done an EICR at a cleaning company today. The installation is less than a year old as they have had a refurb. The spark who did was retired and wouldn't issue any certification! In fairness the job is to an ok standard but there isn't any RCD protection on anything. Am i correct in thinking that because it was 'designed' under 7671:2018 that it is a C2? or would C3 still cover it?
Hi Everyone.
The date it was designed has absolutely nothing to do with how safe or dangerous it is.
You need to make that judgement.
Dates are wholly irrelevant.
Reply to EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...