paulwalldall

Hi. Niece had an inspection prior to letting out her house and recieved a number of C2 decisions on earthing. such as "earth cable to TN-S not large enough." Wants to change to 16mm. no bonding to inlet services at all. (fair enough on this one). Question is , Ive only qualified after 3yr course at college (i,m 45 yrs old) got 2394 , inspection testing, got multitester and tools. If i do the changes so it "complies with current regs" would i have to be registered with local authority or niceic or can the chap come back , re-test and tick the boxes. Quick answer appreciated as going out very soon.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

nothing to stop you doing the remedials, then do her a EICR with no C2's, or complete a EIC for the remedials and reference to the existing EICR.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

hoping to see that. good idea to ref old eicr. thanks
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

Why is the 16mm earthing conductor required?
Has the Inspector done an adiabatic to confirm that 16mm is required?
Have a read of 543.1.4, do a PFC and PEFC, then work it out, and I'd bet a 16mm earthing conductor will not be necessary.

You will need to put in some bonding for gas/water/other services.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

don't be messing about with the clamp for the main earth, if it does turn out that it needs replacing then phone the dno and they'll upgrade it.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

I can almost guarantee that the main earth doesn't need upgrading. The only way this would be so is if the OP had either an extremely high PFC or an extremely low PFC. Neither case is likely.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

Any chance of a pic I bet its from the MET to the CU that he has given the code 2 and post 4 has answered that issue.

Out of interest did he refer to any regulation and on the Condition Report Inspection Schedule which item number did he highlight and put C2 against ?
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

I'm concerned about the title of the thread, how exactly was the report refused for a C2?
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

he's only miffed because he wasn't included in HHD's hall of fame.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

must have missed that, laffing so much, my bad.
 
Re: EICR report refused for C2 condition of earthing. How to rectify if i even ned to

Thanks for replies. having seen the house today as i live 60 miles away. i can confirm the earth requiring upgrading is indeed from the incoming supply to earth terminal in cu box. it looks only 6mm at the mo so will do sums to see if acceptable but not sure of breaker types or ze from here. as for bonding to gas/water, checked where supplies are and gas is out front of house and water in the back in kitchen cupboard, cu in dead center of house under stairs. just curious but can i bond to gas pipe as it enters rear of house near to water supply as its a lot easier.(sounds a bit lazy). its only feed is into kitchen then rear of house for boiler.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR report refused for C2 condition of earthing. How to rectify if i even ned to.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
paulwalldall,
Last reply from
paulwalldall,
Replies
25
Views
2,896

Advert

Back
Top