C

ChrisElectrical88

Christ Im now as bad as the others.

Doing a EICR today and every bloody smoke detector was installed about 100mm away from the light. Conventional FA System with series 65 Smokes and Heats. I know building regs say 300mm distances from lights and walls. I know Aico mains smokes instructions say 300mm from walls and lights but I can’t find Series 65 instructions online or anything in 7671. Ita more to note it than code it as the fire alarm bloke should be picking it up on his 6 monthly inspections but isn’t.
 
Just put it as a comment on the EICR, no code, just a written comnent, bonus points if you can pull something over from the relevant 5839 part/clause.

While not part of the EICR, you're CYA by noting and directing, even though it's not on the 7671 scope, doesn't mean we shouldn't be pointing to the proper bits where relevent
 
Just put it as a comment on the EICR, no code, just a written comnent, bonus points if you can pull something over from the relevant 5839 part/clause.

While not part of the EICR, you're CYA by noting and directing, even though it's not on the 7671 scope, doesn't mean we shouldn't be pointing to the proper bits where relevent

Im hoping someone will tell me where in 5839 to look so I can stick it in the notes ?. Cause I can’t find it for love nor money
 
You say a conventional Part 1 system?
 
The smoke detector should not be closer than twice the depth of the light fitting. So if the light fitting is 100mm deep from the ceiling then the detector must be sited above 200mm away.
 
Maybe the Fire Alarm bloke is picking it up and noting it to CHA, but no-one is taking any notice or doesn't want to spend.

Found this here, damn beaten to it,


Detector Fire location.PNG
 
Maybe the Fire Alarm bloke is picking it up and noting it to CHA, but no-one is taking any notice or doesn't want to spend.

Found this here, damn beaten to it,


View attachment 59479
The fire alarm bloke isn’t, this HA don’t mess about, if there told something needs doing it’s just go ahead. He also hasn’t noted the supply is wired in twin and earth, it’s wired on the same circuit as several other items, it’s got no fire alarm do not switch off stickers, it’s got no double pole isolation.
My knowledge of fire alarms is limited as you might be able to tell, but I’m sure I’m right that the above items all need attention.
 
Sounds par for the course fitted by someone who probably has never seen BS5839:1.
[automerge]1594827468[/automerge]
For a Part 1 system it is 500mm from walls and similar obstructions.
 
Last edited:
Some photos of the lighting circuit on the EICR I found. Didn’t get a R1+R2 at every point surprisingly enough.
 

Attachments

  • E759D9CF-855F-4F6B-A00A-D8093604C3E9.jpeg
    E759D9CF-855F-4F6B-A00A-D8093604C3E9.jpeg
    137.4 KB · Views: 72
  • EF95891D-5468-41EC-A0CC-290B79DB71D3.jpeg
    EF95891D-5468-41EC-A0CC-290B79DB71D3.jpeg
    68.1 KB · Views: 63
  • 8D2BFFEB-F7D7-4244-8472-7728DEC7190C.jpeg
    8D2BFFEB-F7D7-4244-8472-7728DEC7190C.jpeg
    104 KB · Views: 73
  • 6226A1C2-4EFE-4428-832D-5F4A14E99F77.jpeg
    6226A1C2-4EFE-4428-832D-5F4A14E99F77.jpeg
    94.3 KB · Views: 72
  • C6714DF2-9CEC-4A02-847D-E4BB3BA6A365.jpeg
    C6714DF2-9CEC-4A02-847D-E4BB3BA6A365.jpeg
    255.3 KB · Views: 73
  • 8F44A896-EC4C-4235-9F6B-16C01A73B8C1.jpeg
    8F44A896-EC4C-4235-9F6B-16C01A73B8C1.jpeg
    118.7 KB · Views: 69

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR Smoke Detectors
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
ChrisElectrical88,
Last reply from
ChrisElectrical88,
Replies
10
Views
3,973

Advert