Can you believe some idiot ,put on their report that a 4mm cable that supplies a cooker circuit,needs to be rewired in 6.0mm,there are 2 cookers in place each cabled in 4 mm.
The rewire would completely mess up all decorations & difficult to do.The rcbo that protects these circuits are both b type 32 amp.Im refusing to do this job,the premises are about 30 years old,& I have no problems with this arrangement,would you feel the same,cheers.
 
What's the installation method of the 4mm cables? what's the KW rating of each cooking appliance?
 
There is a trend nowadays for folk to over rate cables just in case. Not an issue normally for new cables as it allows future extra capacity. But some times you need to do the maths and go by what's needed not what maybe needed.
The current circuit protector is suitable for the cable and the current usage isn't tripping the breaker. So all good.
 
There is a trend nowadays for folk to over rate cables just in case. Not an issue normally for new cables as it allows future extra capacity. But some times you need to do the maths and go by what's needed not what maybe needed.
The current circuit protector is suitable for the cable and the current usage isn't tripping the breaker. So all good.
Cheers,like you say,you would use 6.0 mm these days,but 30 years ago 4.0 mm was adequate.
 
Ah. Ok so I would apply diversity to each cooker.
That makes 16.4A per cooker (@230v)'
Total demand for both is therefore greater than the protective device of 32A.
If you were doing this as a cable calc exercise in college then you would make it 6mm with a 40A MCB.

In practise it's just ok, very tight though.
 
Cheers,like you say,you would use 6.0 mm these days,but 30 years ago 4.0 mm was adequate.
Yes, but 30 years ago it was sized for one cooker. Now someone has added a second one. They have added not just an additional fan oven, but it is a full blown cooker with 4 hob rings and a grill and an oven.
 
The OP stated each cooker was wired in 4mm. "there are 2 cookers in place each cabled in 4 mm"
And that both RCBOs are 32A so implies each cooker is on its own 32A breaker.
 
Can you believe some idiot ,put on their report that a 4mm cable that supplies a cooker circuit,needs to be rewired in 6.0mm,there are 2 cookers in place each cabled in 4 mm.
The rewire would completely mess up all decorations & difficult to do.The rcbo that protects these circuits are both b type 32 amp.Im refusing to do this job,the premises are about 30 years old,& I have no problems with this arrangement,would you feel the same,cheers.
So you decide to call them idiots because you feel they have used incorrect judgement, well I agree with them.
 
Does the cable have to be replaced? Is it underrated for its current use?
If its unsafe (can't see how it is if its on a 32A RCBO) then yes it has be replaced.
 
As Lee says what are the installation methods for these cables, doing an EICR it is hard to judge unless you can see the full run of the cable. I find it difficult to believe, although not impossible these cables would actually comply. Bet the op would rewire them if it were a straightforward task, no questions asked.
 