- Reaction score
- 25,511
Yes those ratings are for clipped direct or for a cable in masonry with no mechanical protection. If the cable is contained in oval conduit then the rating is greatly reduced. But I suspect you are not really interested in alternative opinions.Cable size Rating in Amps
1mm 15
1.5mm 19.5
2.5mm 27
4mm 36
Rating of t/e cabling