i'll post my tuppence worth. 2 possibilities...
1. insulation poor betweem Live and Earth in the switch box, or at the light. some voltage leaking to the metal of the switch plate, causing a shock but insuffient current to trip breaker.
2. dead short at switch or light. shock but not fatal if your body was not earthed.
a trapped cble could cause either of the above but cleared when electrician undid and refitted.
either way, as said previously, the metal faceplate must be earthed. earthing the back box as well is optional (since circa 2004).