Discuss electrical help please in the Industrial Electricians' Talk area at ElectriciansForums.net
M
markco
if a customers boiler has broken and a new boiler is installed i reconnect the new boiler and do a test but do i have to put it on an rcd and upgrade the main bonding or can i just list it under comments on the mwc as i have been told about 3 differant things im confused please many thanks
you wouldnt have to put it on an RCD because it was installed to previous and you will just be reconnected into the FCU/DP switch right ??
the bonding is a grey area - it should definatly be cross bonded (easy enough to do). If the main bonding is in 6mm it can be left as is it is and a note made on the cert. always better to upgrade but not alway practically possible
As you are the last person responsible for messing with that persons electrics you should leave it in an acceptable state but only the stuff that you touch. A boiler is not a piece of portable equipment unless you want a bad back so you're not supplying a new circuit ( anything controlled by its own fuse) If it's in the kitchen you might have to notify LABC. If it doesn't have an RCD to start with why 8ugger about fitting one? PLEASE though do your supp bonding
wot if there is no main bonding at all and i phoned my govening body and they said put it on an rcd as i was the last one to touch it,thanks for helping anyway
i would recomend doing the bonding and fitting a rcd after all as your the last to mess with it just becaue it would cost u a few bob or because u couldnt be arsed when the council told u to trythis for size 15 yrs in the nick if things went wrong and you didnt do eveything possible in a court of law
But all your doing is connecting the flex from the boiler into the FCU, so y the RCD?? BS7671 states that you cant leave it in a worse state, which your not, and your not altering the wiring or characteristics of the circuit.
As regards bonding - I would certainly throw some 10mm to the Gas and Water. and cross bond at the boiler
You would test the Zs at the spur and make sure it was in spec with the allowed value given by BS 7671-2008 for the protective device installed at the source. At least then you would know if it was going to operate the device within 0.4s for TN or 0.2 for TT should a fault condition arise.
There are multiple factors when carrying out these types of work, type of supply at origin, type of device for the circuit, bonding conductor size and so it goes on.
If you were carrying this job out under the NICEIC guidelines you would also have to complete a minor works certificate which asks you all these questions to keep you on the right side of the law.
Hope this helps or confuses ??
Reply to electrical help please in the Industrial Electricians' Talk area at ElectriciansForums.net
Help please! Got this to use as a doorbell but unsure of specifics and wiring. If someone could maybe help with a diagram/specific parts or even...
Had a new unvented Boiler fitted as the old one had reached the end of it's life. Electrician mentioned that it might be worth replacing my fuse...
Guidance please - C&G L3 electrical installation - Hotel extension project Hi folks, I am fairly new to this forum but it looks like the...
Hello, I would like electrical advice please. I recently started a new cleaning job. I have been asked to use a Shark Steamer. The floor I am...