Discuss Electrical safety concern notification for dummies in the UK Electrical Forum area at ElectriciansForums.net
Wez
Hi guys. I've recently purchased a new property and the following notice was left for me. Does anyone have the right lexicon to explain this to a complete novice?
As a side note, My oven always trips the fuse box and doesn't work, yet all the other electrical circuits are fine - could this be linked?
How tall is the bathroom?
Re the Oven - sounds like that is the issue, not the wiring.
Are there any more pages in the "report" left for you?
Your bathroom lights arent capable of withstanding water, splashes etc. Zones can be found here
Best bet is to check the zoning with a tape measure, then get a spark in, change the light fittings to correct IP rated ones for the zone and whilst he is there ask him about the suplimentry bonding requirement.
Is your oven gas or electric? does it trip on hobs or just oven? does it trip the MCB or RCD? (google the pics)
So in essence, the bathroom is divided into zones. Zone 0 is the bathtub/shower tray. Zone 1 is the area directly above zone 0 to a height of 2.25m above the finished floor level and zone 2 extended horizontally 0.6m from the edge of zone 0 and zone 1.
Within these zones, only certain types of accessories/installation methods are allowed.
This report suggests you have non IP rated downlights within Zone 2. This means water could get into them and present a hazard. The important thing to note is if they are in the ceiling and that is higher than 2.25m from finished floor level, they are not within zone 2, they are classed as outside the zone. Should you fit non-IP rated downlights in a bathroom? common sense says no, but if they are outside the zones they do not contravene the regulations.
The issue about supplementary bonding... if you have RCDs and all circuits that would need supplementary bonding (more on that in a moment) are protected by them, then you don't need supplementary bonding. Circuits that should be included in supplementary bonding are any that supply accessories within the bathroom, so typically your lighting circuit and say an electric heater circuit. Supplementary bonding connects the earths of these circuits to the exposed metalwork in the bathroom to create an local equipotential zone, the purpose of this is to minimise the potential difference between different items of metalwork, thus minimising the chance of you being killed in the event of you touching two different bits whilst an earth fault is present.
The oven is a separate issue to the issue of the bathroom electrics highlighted by that report.
Hope that helps.
Hi mate. Thanks for the reply. My light switch for my bathroom is outside the room. The hob is electric and it works fine. As soon as I switch the red button on the wall to allow the oven to work (can send pic but assume that makes sense), it switches the RCD off immediately as soon as I try and use the oven.
There are no more to this specific report, but I had a separate report which highlighted a similar issue. Have attached photo
Sounds like a fault with the cable from the oven switch to the oven or the oven itself. Has it ever worked?
If you could, post a picture of your consumer unit.
Photo attached. Pointing to the one that trips upon use. It's never worked for as long as I've known but recent purchase
You could have a fault between switch & cooker. As the cooker is new, might have a fault in itself, or could be just some damp in the elements.
As others have said, think your electrical installation needs some attention. If you paid for the EICR, you could seek advice from the author.
OK - so my advice would be to ask your friends and neighbours for recommendations for local sparks then show them the 2 reports and get them to investigate further................. don't go rushing to change lights etc until you know exactly what you are dealing with?
Could you post the page of the report with all the circuits listed and the test results?
So, aside from the C3 item with no description, you appear to have a few issues that need attention.
Metal faceplates with no earth
Non-IP rated downlights in Zone 2 (although you should measure your ceiling height and check whether it's less than 2.25m - if it is, you should look to improve it, if not then it's up to you, but being sensible, IP rated downlights in a bathroom would be an improvement)
No supplementary bonding
A fault with your oven
Possible solutions:-
Metal faceplates with no earth - If you want to be safe, have them changed for plastic face plates or have them checked to see if there is a CPC available. On a report, some people just report, others fix minor issues... it could be the CPCs are there and just need connecting (personally I would have just connected them and mentioned it as a note on the report if there weren't too many of them)
Non-IP rated downlights - Check the ceiling height and take it from there
No supplementary bonding - You could have supplementary bonding added or alternatively (if they'll fit) have the two lighting circuits circuit breakers changed to RCBOs, which would then provide the required RCD protection and render the lack of supplementary bonding a non-issue
Oven fault - Have the fault investigated by a spark with the right test gear
My advice is, get a spark in to have a look at these issues and give you a quote for sorting them out. If you asked me to do it, the solutions I've outlined above would be my initial thoughts. As @Murdoch suggests, try and get a recommendation for a spark from family, friends or colleagues.
The cooker is relatively old. I intend on replacing it. That might sort the issue?
Unless the fault is betwixt cooker switch & outlet plate. Disconnection of oven, might prove or disprove that.
As others have said, I think you have some more pressing issues, rather than not being able to cook your diner?