Hi

Employed electrician to wire extra sockets in bedrooms upstairs in an empty house. However I have noticed when I lifted floor board up to do other work, that the cables are running through holes close to ends of the joists, not within the safe zones, .25 & .4, as with Building Regs.

Looking for advise on how to approach this, with them.

Thanks
Jazz
 
Get back , show regs, ask them to make good (strap joists with extra timber ?) .Dont pay any balance until done.
Thanks will do, was quite shocked when I saw what they had done, at the time so didn’t now about the regs, but it just looked wrong. It was then I checked on the rules about cutting holes in joists.
 
In the old days I always used to drill my holes about 300mm from the wall, did it this way for many many years. Then someone pointed out the .25/4 rule so I now come in roughly .25 the span
 
The position of the holes will be fine as long as there are no other sections of the same part of the joist removed. Ie notches in the same area of the joist.

The regs are only as they are to give a clear zone for notches and for holes so there is no confusion between plumber/electrician.

Holes always used to be drilled nearer the walls as dusty says.

Sometimes it’s not practical to take up the part of the floor that is over the ‘correct’ section of the joist. It’s often not possible to see the span of the joist until you have access either. Your electrician has potentially done nothing wrong imo.
 
as above. as the joists are c.1970, they will not be flimsy oven baked crappy wood like today's builds and will not collapse when farted on with > 1Nm of metric force per ssquare centipede when the ambient temperature is outside the range 20 -21deg. and the humidity is above 60%.
 
The position of the holes will be fine as long as there are no other sections of the same part of the joist removed. Ie notches in the same area of the joist.

The regs are only as they are to give a clear zone for notches and for holes so there is no confusion between plumber/electrician.

Holes always used to be drilled nearer the walls as dusty says.

Sometimes it’s not practical to take up the part of the floor that is over the ‘correct’ section of the joist. It’s often not possible to see the span of the joist until you have access either. Your electrician has potentially done nothing wrong imo.
I agree I would feel hard done by if one of my customers had lifted floorboards and inspecting my routing of cables. I would/Do use existing holes where necessary although I tend to stick to the rule of thumb of 50mm from top or bottom of joist but I certainly don’t stress over routing my cables on existing holes. Not sure who said on here on not paying the spark but that’s ridiculous. Are there any other issues or is it just the routing that your not happy with?
 
How happy would any of you be if a Structural Engineer told you that the size of cable you specified is over the top and can be smaller.

OSG 7.3.1
Yes I appreciate that but drilling new holes surely would make matters worse wouldn’t it? I’m just counter debating ideally 50mm below top or bottom is perfect but using existing holes which have been used in millions of properties throughout the years doesn’t warrant non payment surely or classed as unsafe structurally
 
It's not a 'safe zone', it's a structural strength thing, and in most cases is absolute bo**ox, depending on how the end of the joist is supported
Nothing to do with separating pipes from cables either, since most pipes these days are fitted through drilled holes as well.
 
The 0.25/0.4 thing is a one-size fits all thing... mainly directed at modern construction where everything is as small as it can possibly be. I agree with others on here... a 1970s built property will probably have substantially bigger timbers than a new build (excepting I beam cr@p). I've done alot of work in Victorian terraced houses, and they're even better built !... You could probably remove every other joist in those places and they'd still be stronger than a new build. I've also worked on really old places with solid oak joists that are as hard as granite !

So yes... there's Building Regs guidance... but we also need common sense. (if only it wasn't banned about 20 years ago !)
 
"One size fits all thing" so you know all about overturning moments, bending analysis and the way structural members fail by the twisting moment where compression and tension zones change or are at equilibrium, fascinating.

" I've done alot of work in Victorian terraced houses, and they're even better built !... You could probably remove every other joist in those places and they'd still be stronger than a new build. I've also worked on really old places with solid oak joists that are as hard as granite !" Do you know what joist are for?
 
"One size fits all thing" so you know all about overturning moments, bending analysis and the way structural members fail by the twisting moment where compression and tension zones change or are at equilibrium, fascinating.
As it happens, I have studied these things, and passed the exams at the end, which is why I'm confident in saying that in most cases, especially with conventional timber joists, that the guidance is bo**oxs.
 
"One size fits all thing" so you know all about overturning moments, bending analysis and the way structural members fail by the twisting moment where compression and tension zones change or are at equilibrium, fascinating.
It's been over 30 years since I did my degree in Mechanical Engineering ! I can hardly remember what I did yesterday !!

But I do remember having to use a 'safety factor' of 6 when we designed beams... which always annoyed me.
 
It's not a 'safe zone', it's a structural strength thing, and in most cases is absolute bo**ox, depending on how the end of the joist is supported
Nothing to do with separating pipes from cables either, since most pipes these days are fitted through drilled holes as well.

Correct, It’s not about separating pipes and cables. It’s about separating holes and notches.
 
It was me who suggested holding back any final payment etc .Until we see how badly the new holes etc are .Its only fair to say it could either be minor or bloody dangerous .And it will not be hard to see if they are new holes or old etc . Ive seen terrible "Notching " and holes been done .That if the property belonged to me would annoy me .
 
I really wouldn't stress it, as said the guidelines are relatively recent (used to be just 1 in 6) and I've seen so many examples of far worse that never come to anything - typical one is lazy plumber can't be bothered to lift fresh boards so goes with a line of notches right over sparkys cable run, or removing 3" of joist for a waste.
 
But I do remember having to use a 'safety factor' of 6 when we designed beams... which always annoyed me.
That reminds me of one I had years ago when I rigged antennas, a structural engineer designed a bracket to fit to a building to take a 2.4M dish antenna, the bracket that was designed actually needed a bigger offset from the building than the structural engineer had allowed for so I asked him to revise the calcs for the extra 250mm offset and confirm this was acceptable his immediate answer was that it would not be a problem I pushed him to actually do the calcs and was told that even with the extra offset the bracket would still be at less than 10% of it's maximum load
 
It was me who suggested holding back any final payment etc .Until we see how badly the new holes etc are .Its only fair to say it could either be minor or bloody dangerous .And it will not be hard to see if they are new holes or old etc . Ive seen terrible "Notching " and holes been done .That if the property belonged to me would annoy me .
Fair enough mate I just don’t like it when customers come on here and then will use it against the electrician to not pay just by a single comment. They asked the person in question to carry out the work and therefore should trust his judgement I know there are plenty of cowboys but this particular thread seems like the electrician is being hard done by. Anyhow hope it all gets resolved and it’s not dangerous which I highly doubt.
 
We are promised pics. next weekend, but so far we have been told that they are 25mm holes in 5 x 2, and near the end.
It's difficult to see how this could have any significant affect on the structural integrity of the joists, but I'll wait for the pics.
 
Here are the photos as promised, I’am ok with it as long as it not going to cause me problems in the future.
 

Attachments

  • 44981694-1563-42DF-B236-729DCC5E36ED.jpeg
    44981694-1563-42DF-B236-729DCC5E36ED.jpeg
    575.2 KB · Views: 89
  • 5916F4AD-D0D8-4F41-A70F-3390B6F0BF1D.jpeg
    5916F4AD-D0D8-4F41-A70F-3390B6F0BF1D.jpeg
    739.2 KB · Views: 85
  • 88A195BF-E348-43A6-B354-0349AA5F9ACF.jpeg
    88A195BF-E348-43A6-B354-0349AA5F9ACF.jpeg
    612.6 KB · Views: 88
If that was new work in my house, like you, I wouldn't be happy.

There doesn't appear to be a reason for not putting the holes in the prescribed zones and, unless more cables are to be added, the holes appear to be larger than they need to be.

Was the same electrician responsible for the hole bottom left in the 2nd picture?

As I think Littlespark is alluding to, it's not good practice to run a signal cable such as coax so close to LV power cables.

All that being said, my house (Victorian era) has had many of the joists butchered over the years. Notches and holes out of prescribed zones and often very close together. Holes drilled at a 45 degree angle through the timber. The previous owner took a huge chunk out of a joist under the bathroom as they positioned the shower tray such that the waste outlet was on a joist. So far, the floors are still standing...!
 
If that was new work in my house, like you, I wouldn't be happy.

There doesn't appear to be a reason for not putting the holes in the prescribed zones and, unless more cables are to be added, the holes appear to be larger than they need to be.

Was the same electrician responsible for the hole bottom left in the 2nd picture?

As I think Littlespark is alluding to, it's not good practice to run a signal cable such as coax so close to LV power cables.

All that being said, my house (Victorian era) has had many of the joists butchered over the years. Notches and holes out of prescribed zones and often very close together. Holes drilled at a 45 degree angle through the timber. The previous owner took a huge chunk out of a joist under the bathroom as they positioned the shower tray such that the waste outlet was on a joist. So far, the floors are still standing...!I
 
The problem with deviating from guidance is you then have to qualify your choices.

We all know that there is an --- Cover Factor in many regs but if we venture there the onus is on us to demonstrate we have not introduced a hazard.

In solid, dry and rot free joists, like those, I can guarantee those holes will no be an issue but I cannot qualify that statement.

All I can offer is if it were my house I wouldn't be worrying.
 
As the electrician has deviated from the prescribed zones ask for his Hazard Analysis and Risk Assessment, that he obviously did, to satisfy himself that it was OK to do so.
 
As the electrician has deviated from the prescribed zones ask for his Hazard Analysis and Risk Assessment, that he obviously did, to satisfy himself that it was OK to do so.
Come off it Mike. Everyone here, including yourself, knows those joists aren't going to collapse.

To the OP: Of all the sins an electrician can commit, this is about as minor as it gets. Put the floorboards back down, and don't worry about it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
West Midlands
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Electrician has cut holes to close to joist ends
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
47
Unsolved
--

Advert

Thread statistics

Created
JazzyB,
Last reply from
LukeD,
Replies
47
Views
6,491

Advert

Back
Top