Got called to a house today, they claim to be having problems with the electrics tripping.
had 2 problems, one was the immersion heater (which I think is the true cause of the problem.
the other problem I had was the RCD was tripping at 24mA on one side and 15mA on the other (ramp test)
Changed the RCD and still had exactly the same readings 24/15
also the RCD was giving me >2000 on 1/2 test.
Had me stratching my head a little till I guessed what it was
ps all cables were clear on insulation
see who guesses the correct answer 1st
 
The more than 2000 is correct as it is not tripping when 15mA is injected into the circuit so it times out at 2 secs.
Are you useing a Megger by any chance!
 
As far as your ramp test are concerned 24 ms is fine but the 15 is on the limit.

Where you testing with loads connected by any chance ?


Sent by my Hoover 234 talkpad
 
Last edited:
Yes using a megger
Possibly I didn't explain clearly, I know > 2000 is correct, but i shouldn't have tripping readings of 24/15 on a ramp test if it's ok on 1/2 test,
 
Well I was expecting about 22 on both sides
sorry I just realised how I now made myself clear - I am talking about tripping current not tripping times. The RCD is tripping at 15mA
 
i don't understand what you mean by7 both sides. a ramp test gives 1 reading.
 
Kevin what model Megger are you useing if its the 1550 range you can't Ramp test on both sides of the waveform on AC.

Your not on the DC mode by any chance?

Had me stratching my head a little till I guessed what it was
ps all cables were clear on insulation
see who guesses the correct answer 1st

You will have to tell us the answer because I am a little confused don't know about Tel mind you.


Regards

Tony
 
I had this on my Mertial Tester the other day - had the wrong wave set on my tester.

Changed the wave over and all working fine now
 

Reply to Electrics tripping ( on going problem) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
753
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock