Do they sustain illumination with the test facility for a period of time say 10 minutes.
Yes because they have just had new batteries.Do they sustain illumination with the test facility for a period of time say 10 minutes.
What Tel said^^^^^^^^^^^^^^^^^^^^^try turning off the MCB again and see if the green mains LED is still on. this would indicate that they were fed from elsewhere.
the light kicks in on EL flick test, but not when the mcb is switched off.
If they're non maintained and work on the flick test then they will work in a power cut.
You must be switching the wrong MCB off.
But he also stated that the green indicators are normally on, and switch off when in test.
Depending on where the board is they may illuminate for a short period then have failed by the time he gets there. He may only be flicking the test facility quickly but need more info and he seems to have gone.
May have replaced batteries due to previous failure when in fact that wasn't the issue, like you say maybe no permanent supply or the fiitings have duff charging parts.It's seems unlikely if they have new batteries, but of course is not impossible.
Have they ever worked properly
100 percent the correct mcb as all the lights in that corridor go off when the power is cut.If they're non maintained and work on the flick test then they will work in a power cut.
You must be switching the wrong MCB off.