The lights illuminate when the test switch is operated.
The lights do not illuminate when power to the entire installation is lost, ie. a power cut.

That is not likely to be caused by the lights being fed from a different circuit.

My guess would be that the test switch is incorrectly wired so that it is connected to the switched live terminal thus switching the light on rather than simulating a power failure.
If this is the case then it probably doesn't have an unswitched supply at all and so the battery hasn't been charged.
 
the light kicks in on EL flick test, but not when the mcb is switched off.

If they're non maintained and work on the flick test then they will work in a power cut.

You must be switching the wrong MCB off.
 
If they're non maintained and work on the flick test then they will work in a power cut.

You must be switching the wrong MCB off.

He has stated that they did not work in a power cut.

Don't assume that the test switch has been wired correctly,
 
  • Like
Reactions: Davisonp
But he also stated that the green indicators are normally on, and switch off when in test.
 
Depending on where the board is they may illuminate for a short period then have failed by the time he gets there. He may only be flicking the test facility quickly but need more info and he seems to have gone.
 
Depending on where the board is they may illuminate for a short period then have failed by the time he gets there. He may only be flicking the test facility quickly but need more info and he seems to have gone.

It's seems unlikely if they have new batteries, but of course is not impossible.
 
The OP doesn't say explicitly that the charge indicator goes off when the test switch is operated, only that it did when the supply was pulled. The only consistent explanation seems to be Davesparks'...
 
  • Agree
Reactions: Davisonp
It's seems unlikely if they have new batteries, but of course is not impossible.
May have replaced batteries due to previous failure when in fact that wasn't the issue, like you say maybe no permanent supply or the fiitings have duff charging parts.
 
Depending on where the board is they may illuminate for a short period then have failed by the time he gets there. He may only be flicking the test facility quickly but need more info and he seems to have gone.
Nope, i can see the lights from the consumer unit and watch the lights when i switch them off.
 
Hmm. If the green LEDS stay on when the test switch is operated, the wiring is wrong as per Davesparks' suggestion but the fact the LED is on should indicate reliably that the battery is on charge, not merely that the PL is live. So although the test switch would not test the fitting in the intended manner, if the battery is good then the fitting should still function during power loss. If the green LEDs go off when the test switch is operated, then there's no evidence of a wiring error and again the fitting should still work.

I think we've gone as far as we can go with the evidence available and investigation with test equipment is now needed to make any useful progres...
 
  • Like
Reactions: Rpa07 and DPG
Depending on where the board is they may illuminate for a short period then have failed by the time he gets there. He may only be flicking the test facility quickly but need more info and he seems to have gone.
Nope, i can see the lights from the consumer unit and watch the lights when i switch them off.
Which could just be the lamp obscuring the LED
The green led is illuminated and goes off when flick tested and mcb switched off.
 
So test facility operates them all but the mcb does not even though all the charge leds extinguish when the mcb is off.
 
  • Agree
Reactions: 1 person
Hmm. If the green LEDS stay on when the test switch is operated, the wiring is wrong as per Davesparks' suggestion but the fact the LED is on should indicate reliably that the battery is on charge, not merely that the PL is live. So although the test switch would not test the fitting in the intended manner, if the battery is good then the fitting should still function during power loss. If the green LEDs go off when the test switch is operated, then there's no evidence of a wiring error and again the fitting should still work.

I think we've gone as far as we can go with the evidence available and investigation with test equipment is now needed to make any useful progres...
Yes thanks everyone, our contractors are coming in Monday to take a look as they have done some work on the lights. I thought i would put it out there just in case there was an easy fix without me calling them.
 
Let us know the outcome it is most intriguing.
 
  • Like
  • Agree
Reactions: Rpa07 and DPG
Interesting post. As previously commented on by others. I'd be looking into the key switch possibly switching incorrectly perhaps the switch feed, strange that although the battery is charged it does not illuminate when power is cut.
I've previously seen like for like lamp changes cause electronic ballasts to become faulty on em lighting. They can be high maintenance sensitive bits of kit
 

Similar threads

F
Replies
0
Views
106
Electricians Jobs
findajob.dwp.gov.uk
F

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Emergency lighting help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
Jon West,
Last reply from
Stspark,
Replies
37
Views
3,402

Advert