A property I am working in suffers from regular power cuts and energy spikes.

The property is the last on an overland supply, ( up on the hills).

I suspect that this supply problem is the cause of certain electronically controlled items being damaged beyond repair.

Is there something that could be installed in the property by an Electrician to help prevent this repetitive failure or is it something that is the responsibility of the supply company / DNO?

Are they supposed to supply a consistent Voltage or is being at the end of the line just tough luck?

How do they view it and what are their responsibilities?
 
How do you know there are "energy spikes" , how do they present and what exactly are you describing?
Power cuts on rural overhead lines are unfortunately one of the downsides of rural living, but depending on your reply to my question, you may really need some power analysis on the incomer to see if there are any minute to minute, hour to hour, day to day quality issues with the supply
 
How do you know there are "energy spikes" , how do they present and what exactly are
How do you know there are "energy spikes" , how do they present and what exactly are you describing?
Power cuts on rural overhead lines are unfortunately one of the downsides of rural living, but depending on your reply to my question, you may really need some power analysis on the incomer to see if there are any minute to minute, hour to hour, day to day quality issues with the supply


Well the fact is I don't 'know' that there are spikes, that conclusion was arrived at by the powers of deduction by the pump manufacturers, which could of course be miles off the mark.

Long story short:-
I installed a Grundfos Pump / Circulator, some 15 years ago and it has run everyday since. Eventually pump fails (water issue, not the pump), so it was replaced with new pump.
The new pumps (you may know) are all ERP compliant and run off electronic components as opposed to a simple motor and capacitor.

After a few months the pump failed following a power cut and I spoke to manufacturers regarding this matter. They said that they had, had issues with a component part in the model I had installed which was very sensitive to energy spikes. They said that a drop or surge in power would damage this particular component and It would be better to use a different model ( with internal suppressor). I did that, they supplied it FOC.

This new model has also had issues (following a power cut which I suspect caused his oil burner to lock out) and the Manufacturers say it must be down to the supply voltages being erratic, the pumps are designed to work on a fairly constant 240V.

So to sum up, the energy/voltage spikes may not exist and I am not one for getting involved with the electricity supply side of my job. I just wanted to know if there were any suggestions I might make to help the customer out, as in, can he contact the supplier and ask them to test the supply? will they do that? or is it like you say, one of the downsides to being in the middle of nowhere.

As far as the pump goes, that is now resolved and I am happy he will have no further issue with that.
 
Voltage peaks are not unusual after a power outage which can last for as little as a nano second, you could resolve this by fitting a voltage optimiser/regulator but these are expensive and "may" only solve an external issue. Appliances used at the property can also cause issues but not normally enough to affect other alliances. Do they get much lightening?
 
Useful background LP, thanks. I've heard of various problems with "new" style pumps.
Given the pump problem is now solved, it's probably not worth having a power analysis carried out - I suspect most DNOs would argue that rural o/head lines are particularly susceptible to voltage variations. That said, if problems are experienced in good weather conditions, I would be tempted to get an analysis done. Be aware that suitable analysers are not in every ( most) electrician's kit.
 
Voltage peaks are not unusual after a power outage which can last for as little as a nano second, you could resolve this by fitting a voltage optimiser/regulator but these are expensive and "may" only solve an external issue. Appliances used at the property can also cause issues but not normally enough to affect other alliances. Do they get much lightening?

No more lightening than anyone else, no !
 
Useful background LP, thanks. I've heard of various problems with "new" style pumps.
Given the pump problem is now solved, it's probably not worth having a power analysis carried out - I suspect most DNOs would argue that rural o/head lines are particularly susceptible to voltage variations. That said, if problems are experienced in good weather conditions, I would be tempted to get an analysis done. Be aware that suitable analysers are not in every ( most) electrician's kit.

Thank you.
 
Voltage peaks are not unusual after a power outage which can last for as little as a nano second, you could resolve this by fitting a voltage optimiser/regulator but these are expensive and "may" only solve an external issue. Appliances used at the property can also cause issues but not normally enough to affect other alliances. Do they get much lightening?

Thanks for that. The power cuts are only minutes. I was expecting it to be a TT out there but it isn't it's TNCS.
 
No more lightening than anyone else, no !
but if it's an overhead line then the impact of any nearby lightning strike will be far far higher than for areas with underground supply lines.

Have you checked the Ze? I've seen issues before in similar settings where there was a very high resistance joint on a neutral connection on the suppliers side. Also check the neutral connections in the internal wiring as the same applies.
 
but if it's an overhead line then the impact of any nearby lightning strike will be far far higher than for areas with underground supply lines.

Have you checked the Ze? I've seen issues before in similar settings where there was a very high resistance joint on a neutral connection on the suppliers side. Also check the neutral connections in the internal wiring as the same applies.

Not checked ze no. Only tested earth loop and volts on immersion heater when it was changed last week.

Going back at some point over the coming weeks so I will check that when I return, out of curiosity.
 