Just a wee update for ye
Networks came out. They couldn’t open up the wall. Said I was to do it but they will request permission from their supervisor to do this tomorrow.
As a result they couldn’t do all of their tests. However initially, the one of the live cables into the meter was damaged so needs replacing, neutral at meter was good but they’re not ruling out any damage of cables behind the wall.
Although they believe it’s unlikely a fault on their end…
Will see when they return tomorrow
We did another test today to find that when EV charger runs, we get 4-5 amps on the earth cable.
EV charger is disconnected now until source of issue is found