That appliance should have been earth bonded but it wasn’t. Perhaps why it was the victim or some other strange reason.
It's a likely contender if it is connected to metallic water or gas mains that were providing the best earth path after the CNE broke open. As you say, adequate main bonding would then have prevented damage to the wiring by diverting the current along a much heavier conductor. But... would you have discovered the problem in that case, or would the pipework have been left carrying the entire house load current for the foreseeable future?
Some of us here are not huge fans of TN-C-S, even in its PME guise.