I have just installed my first EV Charger yesterday. I have installed using a 6mm twin from the non RCD side of the consumer unit on a 32a type b MCB. The length of run is around 5 metres and is contained in 20mm round conduit.

The charger I have fitted is a Rolec with a built in type A 30mA RCBO. I have installed an earth rod below the charger as I was told EV chargers can rely on the earth of a TNC-S system.

Upon testing j had a reading of 347 ohms on my Rod and 24.8ms on my RCD. my question is, would this be sufficient as it is protected by a 30mA RCBO therefore the maximum reading permittable is 1667ohms or am I wrong and does it have to be below 200ohms?? 50volts (touch voltage / 0.03 = 1666.66.

Thanks guys! Go easy, this is my first post!
 

Attachments

  • IMG_20201107_143831.jpg
    IMG_20201107_143831.jpg
    228.1 KB · Views: 101
He has an i3. Would you suggest banging another rod in then??
Is it the sort of rod that you can use a joining piece and add another length to it to bang in?

Generally a deeper rod is more stable against frost or drought changes than the equivalent of two shallow ones. That is the reason for the 200 ohms mentioned in 18th Table 41.5 (also citing 542.2.4) even though a 30mA RCD is theoretically OK with 1667 ohms.
 
Is it the sort of rod that you can use a joining piece and add another length to it to bang in?

Generally a deeper rod is more stable against frost or drought changes than the equivalent of two shallow ones. That is the reason for the 200 ohms mentioned in 18th Table 41.5 (also citing 542.2.4) even though a 30mA RCD is theoretically OK with 1667 ohms.
Hi mate. No it is not one you can add an extension onto it ?. I read up in the regs regarding the 1667ohms if protected by a 30ma RCD. So would this reading of 347ohms be sufficient??
 
I have just installed my first EV Charger yesterday. I have installed using a 6mm twin from the non RCD side of the consumer unit on a 32a type b MCB. The length of run is around 5 metres and is contained in 20mm round conduit.

The charger I have fitted is a Rolec with a built in type A 30mA RCBO. I have installed an earth rod below the charger as I was told EV chargers can rely on the earth of a TNC-S system.

Upon testing j had a reading of 347 ohms on my Rod and 24.8ms on my RCD. my question is, would this be sufficient as it is protected by a 30mA RCBO therefore the maximum reading permittable is 1667ohms or am I wrong and does it have to be below 200ohms?? 50volts (touch voltage / 0.03 = 1666.66.

Thanks guys! Go easy, this is my first post!
I would not be happy with that reading . You should be attempting to get the reading as low as possible within a budget . This week we installed a similar setup with a 5/8s rod achieving 40 ohms . Last week we used 2 and got down to 20 ohms . Considering a rod and clamp is around £15 its hardly breaking the bank .
 
I would not be happy with that reading . You should be attempting to get the reading as low as possible within a budget . This week we installed a similar setup with a 5/8s rod achieving 40 ohms . Last week we used 2 and got down to 20 ohms . Considering a rod and clamp is around £15 its hardly breaking the bank .
Cheers mate. Not that it's breaking the bank, just that it's in a hell of an awkward location. Gas and electric income within a couple of foot as well as 3 drains ?? I think I will just bang another rod in to be on the safe side but just hoping I don't hit anything!
 
If you already have a rod in and know that particular place is safe, then put in a longer one in its place, maybe using a joining section so each section is manageable.

When I recently put in some 2m x M16 threaded stainless rod for earthing I used a 1m long SDS drill to get down the 1st metre before driving/screwing the rods in - that might help you get a bit deeper with the 5/8" = 16mm style of jointed rod.

If you put in a 2nd rod very close it will make little difference to the Ra value, you really want to be a rod's length away, or ideally two rod's length or more if paralleling rods.
 
Cheers mate. Not that it's breaking the bank, just that it's in a hell of an awkward location. Gas and electric income within a couple of foot as well as 3 drains ?? I think I will just bang another rod in to be on the safe side but just hoping I don't hit anything!
Next time you look at an EV job if rodding is going to be a nightmare order a PEN fault relay and you wont have to use an earth rod .
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
North Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Apprentice electrician. 3rd year level 3 NVQ.

Thread Information

Title
EV Charger
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
Tomosmorris94,
Last reply from
Tomosmorris94,
Replies
26
Views
6,842

Advert

Back
Top