move the 1x socket over to the 2x socket MCB. (16A). then replace the redundant MCB with a 32A. then install your new RFC from that.
 
I see a Niglon CU and a Proteus isolator.
I foresee issues over costs.
what's wrong with that? the proteus isolator is not part of the CU so mixing of makes is not relevant.
 
When did this lazy approach to diversity come in to force? When I was an apprentice you looked at what was actually installed, not counting MCB values and doing a calculation on those.
 
When did this lazy approach to diversity come in to force? When I was an apprentice you looked at what was actually installed, not counting MCB values and doing a calculation on those.
It's the wet blanket culture we live in now mate
 
IMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
 
IMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
I believe the only instant water heater is the shower, I will double check, I will perform a clamp test on Sunday when I'm back there to get a true picture
 
I get why you are fretting over the max demand if you will be taking the NIC guy round on your first assessment but in my experience I have never been asked once about demand etc... they do have some common sense. In anycase think about it for a moment... has the fuse blown with what is currently there?
Also is there any signs of thermal damage to the meter tails?
 
Please forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a
 
Reality check

The diversity "guide" is way out of date and in cases like this (assuming there is no electric space heating) should be ignored.

I'd be surprised if the load per day exceeded 10kw
 
Please forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a
X 0.4 mate not divide by 4 which comes out at 68.8 + the 40......but as before that’s not a realistic way of applying diversity especially in a domestic scenario
 
I normally use the times 4 as a useful rule of thumb, but common spence needs to prevail.

As has already been said having the socket circuits devided between 5 breakers or having them on one breaker would make a massive difference on the total calculated load, but no difference on the actual load.
It's good practice to split the sockets onto a few mcb's but in this scenario itsprobable that the socket circuits are pulling no more than 32A between them.
Do the actual loading for each circuit and find out.
 