Hi guys, I have been asked to fit a ring main in a utility room currently being built with a outside socket and a lighting circuit with 4 led lamps and a outdoor light, this much I am comfortable with.

My issue is with the max demand,
The current consumer unit is loaded to the max with 212amp of mcb's
With a 60amp cut out fuse

So if I do the math 212a -40a x0.4 +40a
Gives me a maximum diversity of 108.8amp

So I'm already nearly twice my max demand already before I've started adding my circuits.

It's a 2 bed small bungalow, this seems hugely over rated, I would like to get my 1st NIC assessment done on this so i want to cover all bases.

So any ideas would be gratefully received, my thoughts would include
1. Request DNO to upgrade to 100amp cut out which would still not meet the criteria,

2. Test and possible down grade any overrated mcb's, there is five circuits for sockets????

3. Full load test

4. Could I apply diversity to each circuit independently ?

Here is the C.U and cut out
20181129_175817.jpg
20181129_175822.jpg
 
Work out the max demand on what is used and connected instead.

If the sockets were arranged on one circuit instead of five would the actual use be less ? If there were 8 circuits would the actual use be more ?

How will downgrading the circuit breakers help the actual use of the installation ?
 
you have got no chance on that .can you not alter any of the circuits to make ring .

That was what I meant on option 2, I haven't seen inside the C.u yet but I can only imagine the majority are run separate in radials, it would possibly undertake some destruction to convert to ring circuits unless I was very lucky but could be a viable option
 
Average night with the lights on, TV going etc you'd be lucky if that hits 10 amps. Add another 40 maximum if the shower is running.
 
Listen to Andy mate,diversity is not just about that single calculation....for instance if 1 lighting circuit is 6a mcb but has 7-8 points at couple of watts (leds) you’re not realistically ever gonna reach 6a,even if you put 100w bulbs in......
You’ve also got 4 radial circuits totaling 72a with 5 sockets on...
 
That’s up to you mate,but bare in mind that you are the one that has to justify your decision and calcs should the worst happen.......engineering judgement my tutor used to call it....I think you’ll be pleasantly surprised if you clamp it though :)
 
I know it's just a small bungalow with the usual domestic appliances that would never even come close to the max demand of the value of mcb's , especially with the old couple that live there, so If I do clamp test and see and prove I have adequate room for movement , would I create space for new socket circuit or just run a sub main?
 
I know it's just a small bungalow with the usual domestic appliances that would never even come close to the max demand of the value of mcb's , especially with the old couple that live there, so If I do clamp test and see and prove I have adequate room for movement , would I create space for new socket circuit or just run a sub main?

You could alter the original circuits as long as you tested and provided certification.
Where would you be running a sub main from and to ?
 
move the 1x socket over to the 2x socket MCB. (16A). then replace the redundant MCB with a 32A. then install your new RFC from that.
 
When did this lazy approach to diversity come in to force? When I was an apprentice you looked at what was actually installed, not counting MCB values and doing a calculation on those.
 
IMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
 
IMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
I believe the only instant water heater is the shower, I will double check, I will perform a clamp test on Sunday when I'm back there to get a true picture
 
I get why you are fretting over the max demand if you will be taking the NIC guy round on your first assessment but in my experience I have never been asked once about demand etc... they do have some common sense. In anycase think about it for a moment... has the fuse blown with what is currently there?
Also is there any signs of thermal damage to the meter tails?
 
Please forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a
 
Please forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a
X 0.4 mate not divide by 4 which comes out at 68.8 + the 40......but as before that’s not a realistic way of applying diversity especially in a domestic scenario
 
I normally use the times 4 as a useful rule of thumb, but common spence needs to prevail.

As has already been said having the socket circuits devided between 5 breakers or having them on one breaker would make a massive difference on the total calculated load, but no difference on the actual load.
It's good practice to split the sockets onto a few mcb's but in this scenario itsprobable that the socket circuits are pulling no more than 32A between them.
Do the actual loading for each circuit and find out.
 

Reply to Exceeded max demand questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
785
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
306
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
768
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
351

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top