Hi guys, I have been asked to fit a ring main in a utility room currently being built with a outside socket and a lighting circuit with 4 led lamps and a outdoor light, this much I am comfortable with.

My issue is with the max demand,
The current consumer unit is loaded to the max with 212amp of mcb's
With a 60amp cut out fuse

So if I do the math 212a -40a x0.4 +40a
Gives me a maximum diversity of 108.8amp

So I'm already nearly twice my max demand already before I've started adding my circuits.

It's a 2 bed small bungalow, this seems hugely over rated, I would like to get my 1st NIC assessment done on this so i want to cover all bases.

So any ideas would be gratefully received, my thoughts would include
1. Request DNO to upgrade to 100amp cut out which would still not meet the criteria,

2. Test and possible down grade any overrated mcb's, there is five circuits for sockets????

3. Full load test

4. Could I apply diversity to each circuit independently ?

Here is the C.U and cut out
20181129_175817.jpg
20181129_175822.jpg
 
move the 1x socket over to the 2x socket MCB. (16A). then replace the redundant MCB with a 32A. then install your new RFC from that.
 
When did this lazy approach to diversity come in to force? When I was an apprentice you looked at what was actually installed, not counting MCB values and doing a calculation on those.
 
IMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
 
IMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
I believe the only instant water heater is the shower, I will double check, I will perform a clamp test on Sunday when I'm back there to get a true picture
 
I get why you are fretting over the max demand if you will be taking the NIC guy round on your first assessment but in my experience I have never been asked once about demand etc... they do have some common sense. In anycase think about it for a moment... has the fuse blown with what is currently there?
Also is there any signs of thermal damage to the meter tails?
 

Reply to Exceeded max demand questions in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top