Discuss Exceeded max demand questions in the UK Electrical Forum area at ElectriciansForums.net

Please forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a
 
Please forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a
X 0.4 mate not divide by 4 which comes out at 68.8 + the 40......but as before that’s not a realistic way of applying diversity especially in a domestic scenario
 
I normally use the times 4 as a useful rule of thumb, but common spence needs to prevail.

As has already been said having the socket circuits devided between 5 breakers or having them on one breaker would make a massive difference on the total calculated load, but no difference on the actual load.
It's good practice to split the sockets onto a few mcb's but in this scenario itsprobable that the socket circuits are pulling no more than 32A between them.
Do the actual loading for each circuit and find out.
 
The existing board only has one RCD. He means replace the board for one which has more than one, and thus performs better re division of circuits etc.
 
I don't think he means put a new board in with only one RCD!
I w
The existing board only has one RCD. He means replace the board for one which has more than one, and thus performs better re division of circuits etc.
The existing board only has one RCD. He means replace the board for one which has more than one, and thus performs better re division of circuits etc.
Took the words out of my mouth DPG!!
 

Reply to Exceeded max demand questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
695
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
741
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
306
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock