what's wrong with that? the proteus isolator is not part of the CU so mixing of makes is not relevant.I see a Niglon CU and a Proteus isolator.
I foresee issues over costs.
It's the wet blanket culture we live in now mateWhen did this lazy approach to diversity come in to force? When I was an apprentice you looked at what was actually installed, not counting MCB values and doing a calculation on those.
I believe the only instant water heater is the shower, I will double check, I will perform a clamp test on Sunday when I'm back there to get a true pictureIMO I would clamp the incoming phase (or neutral) and get some actual readings as from what you have told us your theoretical demand and diversity is way over the top. We know that small domestic installations use on average between 20 - 60% of their maximum demand over the 24hour period. Also, It will depend whether or not you have any instantaneous water heaters installed....
It’s not mixing that’s the proble.what's wrong with that? the proteus isolator is not part of the CU so mixing of makes is not relevant.
Also is there any signs of thermal damage to the meter tails?I get why you are fretting over the max demand if you will be taking the NIC guy round on your first assessment but in my experience I have never been asked once about demand etc... they do have some common sense. In anycase think about it for a moment... has the fuse blown with what is currently there?
No the tails look mintAlso is there any signs of thermal damage to the meter tails?
X 0.4 mate not divide by 4 which comes out at 68.8 + the 40......but as before that’s not a realistic way of applying diversity especially in a domestic scenarioPlease forgive me if I am wrong here and most probably am but wont some electricians add all the MCB's by taking the highest MCB away first which in this case would be 172a divide that by 4 then add the 40a MCB back on which gives a total of 83a